Hi, try to check the OMB\_Time or set al least 1 variable with a lower scanclass than 1 second ( ie. 250 ms )

> [@Modbus TCP disconnection and no reconnection \[SOLVED\]](https://forum.inductiveautomation.com/t/modbus-tcp-disconnection-and-no-reconnection-solved/15689):
>
> Hi, I’m experiencing a problem with ignition v. 7.9.1 ( also recreated on 7.9.4 ) regarding a Modbus TCP connection. I’m trying to estabilish a connection between Scada and an AC500 PM590 CPU from ABB ( also tested with a PM573 ). The onboard ethernet card support something called OMB\_Time, and after looking on internet and on ignition forum, I understood that is closing the tcp connection after a while when no data ( 1000 ms ) is sent from the Scada. So i declared some variables, without using…

---