# Modbus tcp/ip + Power Meter PM5320

**URL:** <https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845>\
**Category:** Ignition\
**Tags:** ignition80\
**Created:** [September 7, 2022, 5:51pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845 "2022-09-07T17:51:35Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![Abdullah\_Abobakr](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/abdullah_abobakr/32/37286_2.png) [@Abdullah\_Abobakr](https://forum.inductiveautomation.com/u/Abdullah_Abobakr)\
**Post date:** [September 7, 2022, 5:51pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/1 "2022-09-07T17:51:35Z")

</div>

Hi everyone,

I have an issue reading Modbus tcp/ip from PM5320 power meter to the gateway ignition, the device connected and provide the status, the configurations looks good as below pictures.

I tried many solution like reverse, base zero (make it true), I have spent a lot of time but it doesn’t work. Any help would be greatly appreciated

 ![1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/2/22ca84559d06f962b46b0403411bb7a1e8aaca6b.png)  
 ![2](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/c/2c82c160a870c339c9449b87235c6853af32842e.png)  
 ![3](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/6/76395c6cad88bba4514cc7ab336719b2ebe49b52.png)

 ![4](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/d/ddf6c80f138f6a8b2bfb0c6a0e5856f8f6032282.png)  
 ![5](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/c/8c012f091f610acbd0e8506cb4e31e0bc9a5eda7.png)  
 ![6](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/4/64d57087aac50f7c28e2ba5d7dad5d8d6761deb1.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 7, 2022, 5:56pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/2 "2022-09-07T17:56:27Z")

</div>

Try setting Unit ID to 1?

Can you read it with other Modbus master software?

---

<div class="post-metadata">

**Author:** ![Billy\_Elliott](https://avatars.discourse-cdn.com/v4/letter/b/c37758/32.png) [@Billy\_Elliott](https://forum.inductiveautomation.com/u/Billy_Elliott)\
**Post date:** [September 7, 2022, 7:27pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/3 "2022-09-07T19:27:36Z")

</div>

I think you have to put the unit number after the name. So the item path would look something like this.  
[PH2MDB4Q0]1.IRUS3000 for the Current A  
On the few I’ve played with they usually have more than one unit at the same IP address, seems like 0 was the network card in the meter, 1 was the meter, 2 was the relay card in the meter.  
When you log into the meter via a web browser there is usually an option to download a spreadsheet with the registers, descriptions, and current values.

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [September 7, 2022, 8:42pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/4 "2022-09-07T20:42:40Z")

</div>

I have a 5560.

Reverse word and zero based both false in gateway.

Voltage L1-N:

```auto
ns=1;s=[PM5560]1.HRF3028

```

---

<div class="post-metadata">

**Author:** ![Abdullah\_Abobakr](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/abdullah_abobakr/32/37286_2.png) [@Abdullah\_Abobakr](https://forum.inductiveautomation.com/u/Abdullah_Abobakr)\
**Post date:** [September 8, 2022, 2:28pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/5 "2022-09-08T14:28:02Z")

</div>

I tried the suggestions above; I think I need to check it at the site since even modbus scan didn’t show data. I appreciate your support guys; I will update you

---

<div class="post-metadata">

**Author:** ![Abdullah\_Abobakr](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/abdullah_abobakr/32/37286_2.png) [@Abdullah\_Abobakr](https://forum.inductiveautomation.com/u/Abdullah_Abobakr)\
**Post date:** [December 21, 2022, 2:29pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/6 "2022-12-21T14:29:29Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/c/3cf1acce1ac8d0d2d0244dec5a225f054a5eee31.png)

Sorry for late update, I solved the issue as the picture above but after that you need to turn off the Power Meter and turn it on again.

---

<div class="post-metadata">

**Author:** ![Zane\_Hansen](https://avatars.discourse-cdn.com/v4/letter/z/919ad9/32.png) [@Zane\_Hansen](https://forum.inductiveautomation.com/u/Zane_Hansen)\
**Post date:** [October 16, 2023, 2:21am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/7 "2023-10-16T02:21:32Z")

</div>

Thanks this information, it has helped me.  
If you can help, where did you find the information to use 255 and Floats starting at address 3000?  
I would like to know what address contains what data.  
Thanks again.

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [October 16, 2023, 10:35am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/8 "2023-10-16T10:35:08Z")

</div>

[https://ckm-content.se.com/ckmContent/sfc/servlet.shepherd/document/download/0691H00000EFUsgQAH](https://ckm-content.se.com/ckmContent/sfc/servlet.shepherd/document/download/0691H00000EFUsgQAH)

> **[PowerLogic PM5000 Series (PM5100, PM5300, PM5500) Modbus Register List |...](https://www.se.com/uk/en/faqs/FA234017/)**
>
>  

---

<div class="post-metadata">

**Author:** ![Zane\_Hansen](https://avatars.discourse-cdn.com/v4/letter/z/919ad9/32.png) [@Zane\_Hansen](https://forum.inductiveautomation.com/u/Zane_Hansen)\
**Post date:** [October 17, 2023, 8:48pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-ip-power-meter-pm5320/63845/9 "2023-10-17T20:48:44Z")

</div>

Thankyou