# Module Referencing Issues on Tag Value Change On Ignition 8.3.6

**URL:** <https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617>\
**Category:** Ignition\
**Tags:** scripting\
**Created:** [August 3, 2026, 3:44am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617 "2026-08-03T03:44:24Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 3:44am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/1 "2026-08-03T03:44:24Z")

</div>

Hi Dear,

I just found out that Ignition 8.3.6 has module referencing issues on tag value changed event.

This is the situation:

i do have modules like:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/2/d2a2f3d9e8241f3b821c3a89e3a260171b1af685.png)

on console script i can reference those module without any error:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/d/fdc07632cd78613bf126ed63d2e4b0be500f6209.png)

but i put the same lines of code inside the tag value changed event script, it would trigger an error:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/5/c51092a34b2b1e84c87dec07b201422714eee87b.png)

i got an error on my logger:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/7/1771d494c53002bdc951226440e61c5b68a7a15e.png)

Originally i did run this on 8.1.26 and didn't get any issue at all.

Just wondering what to do to fix this ?

Regards

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [August 3, 2026, 4:02am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/2 "2026-08-03T04:02:11Z")

</div>

It's considered bad practice to import your script libraries into other scripts in Ignition. It's possible they blocked it in 8.3 but not certain because I don't ever import libraries anywhere else. Reference the functions by their full name everywhere they're used and you'll probably be fine.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 4:24am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/3 "2026-08-03T04:24:26Z")

</div>

Thanks for your feedback. This is what change i made (wrote all namespaces instead of using import statement as seen previously):

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/1/d1311811b5130e5b8eedb10d3eca7055a4be6f52.png)

but i am still getting errors:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/2/c2d2f4d5884708e8156dd86016a3be96b0f57492.jpeg)

This is my constant interval module

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/0/60088fbd8ff73e0cad4b72619119db2609cd3820.png)

Regards

---

<div class="post-metadata">

**Author:** ![justinedwards.jle](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/justinedwards.jle/32/37854_2.png) [@justinedwards.jle](https://forum.inductiveautomation.com/u/justinedwards.jle)\
**Post date:** [August 3, 2026, 5:26am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/4 "2026-08-03T05:26:13Z")

</div>

This is caused when somebody introduces an error into the library script. It's usually a missing colon or mismatched parenthesis.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 5:35am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/5 "2026-08-03T05:35:23Z")

</div>

I am not sure what you meant. But it was working before on 8.1.26. I can't see any syntax error

as i tried to run it on Console Script, it works very well.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/d/5d08deea379b8c3d362754fae4e73e9a3aa93b3f.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/f/1fc6f967f37514969705543f4b7d57694a1b3726.png)

---

<div class="post-metadata">

**Author:** ![justinedwards.jle](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/justinedwards.jle/32/37854_2.png) [@justinedwards.jle](https://forum.inductiveautomation.com/u/justinedwards.jle)\
**Post date:** [August 3, 2026, 5:42am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/6 "2026-08-03T05:42:47Z")

</div>

I have many library scripts and multiple projects. None of them broke when I upgraded to 8.3 ~ _They are currently on 8.3.7_

I have seen this exact error multiple times before when something is goofed in the library script itself. Look along the vertical scroll bar in the interval script for a red rectangle indicating an error:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/f/efc57441626eeb2bcb709029fdb8b3da626e148e.png)

Perhaps somebody missed a colon from one of the classes or functions, or perhaps somebody tried to alternate spaces and tabs when indenting.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [August 3, 2026, 7:53am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/7 "2026-08-03T07:53:36Z")

</div>

Is the specific script included in your gateway scripting project?

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 12:31pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/8 "2026-08-03T12:31:50Z")

</div>

Thanks for your response. But i couldn't find any red indicator as you mentioned.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 12:39pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/9 "2026-08-03T12:39:44Z")

</div>

Yes. if you see my first picture... all the scripts were there. There was no issue when i worked on this project on Ignition 8.1.X then after upgrading my Ignition to 8.3.6 all the sudden the issue came out like this.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/b/5bcfca4cf0359f9701e59939023ff3f38a544048.png)

i called those scripts on CurrentInterval tag value changed event script.

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [August 3, 2026, 1:00pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/10 "2026-08-03T13:00:57Z")

</div>

Value Changed events on tags need to reference your global scripting project. That is what Phil is referring to.

---

<div class="post-metadata">

**Author:** ![lrose](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lrose/32/62724_2.png) [@lrose](https://forum.inductiveautomation.com/u/lrose)\
**Post date:** [August 3, 2026, 1:01pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/11 "2026-08-03T13:01:34Z")

</div>

> [@john.hadikusumo](#):
>
> Yes. if you see my first picture... all the scripts were there.

This does not indicate if that project is configured as the **Gateway Scripting Project**. That's a Gateway Setting.

> **[Gateway Scripting Project​ - Project Library | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.1/platform/scripting/scripting-in-ignition/project-library#gateway-scripting-project)**
>
> Scripts under the Project Library are a project-based resource that allows user created Python scripts to be configured. Objects and functions created in a Project Library script can be called from anywhere in the project. Project Library scripts are...

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [August 3, 2026, 1:02pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/12 "2026-08-03T13:02:18Z")

</div>

What project is configured on the gateway as your gateway scripting project? As @pturmel said, these scripts will need to exist in this project or in a parent to this project for them to work in tag change scripts.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 1:03pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/13 "2026-08-03T13:03:07Z")

</div>

Hi Michael,

This project doesn't has parent project at all.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/7/c76b92d031006915b781daf0a032abfcc38457e1.png)

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [August 3, 2026, 1:06pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/14 "2026-08-03T13:06:40Z")

</div>

So then your gateway scripting project will need to be set as that project where those scripts exist.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 1:08pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/15 "2026-08-03T13:08:48Z")

</div>

They are on the same project.

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [August 3, 2026, 1:09pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/16 "2026-08-03T13:09:45Z")

</div>

Look at the manual that @lrose linked. What project is set there for the gateway scripting project setting?

---

<div class="post-metadata">

**Author:** ![lrose](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lrose/32/62724_2.png) [@lrose](https://forum.inductiveautomation.com/u/lrose)\
**Post date:** [August 3, 2026, 1:14pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/17 "2026-08-03T13:14:46Z")

</div>

I just want to make sure that we are all understanding each other, because, at least to me it is unclear if you have this project set as the gateway scripting project or not.

Here is what we know about your set-up:

1. You are trying to use these scripts in a Tag Change Script.
2. The scripts are defined in the project.
3. There is no parent project for this project.

Because Tags operate outside of a projects scope, the project doesn't need to be running for the tag change to occur, you have to define them in a place that the Gateway knows where they are. This is the Gateway Scripting Project. If the project the scripts are defined in is not set as the gateway scripting project, then the tag system will not be able to locate the scripts which will generate the error you are seeing.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 3, 2026, 1:19pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/18 "2026-08-03T13:19:30Z")

</div>

i think you were right:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/3/e3ce7adb9b1ee2f368ed45a0f664cc56627e615c.png)

My bad, many thanks.

---

<div class="post-metadata">

**Author:** ![john.hadikusumo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/john.hadikusumo/32/75487_2.png) [@john.hadikusumo](https://forum.inductiveautomation.com/u/john.hadikusumo)\
**Post date:** [August 4, 2026, 7:14am UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/19 "2026-08-04T07:14:03Z")

</div>

I think is happening again...not sure what's wrong.

I had set the Gateway Scripting Project to OEE-Launch-Pad

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/e/3e6003c9b8c53681be1ccfc0b53ef1b035485a35.png)

This is my OEE-Launch-Pad project. All scriptings are inside (on the same project).

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/9/79ce576132b38342f6046158561eba49bd012d60.png)

I am getting an error while trying to call the interval modules.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/a/5abb4218a0c691e38194bf80e7f703193ec6850a.png)

No clue what's is going on here. After i switched from OEE LP to OEE-Launch-Pad then it was working. I did some modification here and there, then now the problem comes back.

---

<div class="post-metadata">

**Author:** ![lrose](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lrose/32/62724_2.png) [@lrose](https://forum.inductiveautomation.com/u/lrose)\
**Post date:** [August 4, 2026, 2:29pm UTC](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617/20 "2026-08-04T14:29:49Z")

</div>

You should not be importing any project scripts into other scripts. Full Stop.

If you don't want the admittedly painful need to type out the fully qualified name each time you want to use it then you can just set a top level variable.

```python
INTERVAL = long.path.to.your.script.interval

if someInterval == INTERVAL.HOUR:
    #do something

```

Search the forum and you will find that importing project scripts as you are here opens you up to a whole host of potential issues.

This should clear up your error.

[Next page](https://forum.inductiveautomation.com/t/module-referencing-issues-on-tag-value-change-on-ignition-8-3-6/116617.md?page=2)