> [@sbrannen](#):
>
> In testing, I have (as yet) been unable to cause the bit to latch after well over a thousand mouse clicks whereas I was able to easily cause a latch after just a few dozen clicks without the OPC Read After Write option selected.

Interesting. The failure to write when not checking is far more common that even I thought.

> [@pturmel](#):
>
> gateway-client comms failures, window closure while pressed, and GUI freezes

You are still vulnerable to any of these, and to gateway-plc comms failure at the OPC level.

---