Hello,

I am trying to setup some outgoing communication from different ignition systems and i found on the incoming ignition server i see several have the same common name and serial number, any ideas on how to change those ?  
Thanks

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [September 25, 2024, 11:44pm UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/2 "2024-09-25T23:44:56Z")

</div>

Someone cloned VMs or something.

> [@GAN - How to reset gateway Id/UUID?](https://forum.inductiveautomation.com/t/gan-how-to-reset-gateway-id-uuid/95236/2):
>
> There's a .uuid folder on disk. Nuke it and restart the gateway. Make sure it's not included in your template backup to get a fresh one on each new setup.

---

<div class="post-metadata">

**Author:** ![USR9000](https://avatars.discourse-cdn.com/v4/letter/u/5f9b8f/32.png) [@USR9000](https://forum.inductiveautomation.com/u/USR9000)\
**Post date:** [September 26, 2024, 12:00am UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/3 "2024-09-26T00:00:12Z")

</div>

Thanks, i see two files in linux named ".uuid" under /usr/local/bin/ignition/data/ and another one in /usr/local/bin/ignition/opcua/ . Are these the files that need to be removed?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 26, 2024, 12:01am UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/4 "2024-09-26T00:01:32Z")

</div>

> [@USR9000](#):
>
> and another one in /usr/local/bin/ignition/opcua/

Not this one.

(at least for this issue... they probably shouldn't be duplicated across gateways, but if you remove this you also need to regenerate the certificates)

---

<div class="post-metadata">

**Author:** ![USR9000](https://avatars.discourse-cdn.com/v4/letter/u/5f9b8f/32.png) [@USR9000](https://forum.inductiveautomation.com/u/USR9000)\
**Post date:** [September 26, 2024, 12:15am UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/5 "2024-09-26T00:15:52Z")

</div>

Thanks , this workaround change the Serial number but not the common name, any ideas on how to reset that? the common name is set to "ubuntu", not sure from what file is reading it. None of the linux boxes have the hostname set to "ubuntu".

---

<div class="post-metadata">

**Author:** ![jespinmartin1](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jespinmartin1/32/57175_2.png) [@jespinmartin1](https://forum.inductiveautomation.com/u/jespinmartin1)\
**Post date:** [September 26, 2024, 3:42am UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/6 "2024-09-26T03:42:21Z")

</div>

Make sure that the Gateway Names are different one from another. To restart, request connections and Reset Request

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 26, 2024, 12:04pm UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/7 "2024-09-26T12:04:08Z")

</div>

The OS maintains its own hostname, which is used in new installs to construct Ignition's system name. And the certificates for a system are also files. All of this needs to be regenerated/updated when deploying from filesystem images. There's no shortcut in Ignition itself.

---

<div class="post-metadata">

**Author:** ![USR9000](https://avatars.discourse-cdn.com/v4/letter/u/5f9b8f/32.png) [@USR9000](https://forum.inductiveautomation.com/u/USR9000)\
**Post date:** [September 27, 2024, 8:58pm UTC](https://forum.inductiveautomation.com/t/multiple-incoming-connections-have-the-same-common-name-and-serial-number/96466/8 "2024-09-27T20:58:31Z")

</div>

so the final solution was:

remove .uuid file in ignition/data/  
and the metro-keystore file in ignition/webserver/

with that the Common Name and Serial Number changed on the EAM Controller.