# Need some help/advice on alarming

**URL:** <https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543>\
**Category:** Ignition\
**Created:** [June 9, 2022, 1:13pm UTC](https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543 "2022-06-09T13:13:37Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![Chase\_Viche](https://avatars.discourse-cdn.com/v4/letter/c/e5b9ba/32.png) [@Chase\_Viche](https://forum.inductiveautomation.com/u/Chase_Viche)\
**Post date:** [June 9, 2022, 1:13pm UTC](https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543/1 "2022-06-09T13:13:37Z")

</div>

So we have alarming that can be acknowledged by the main operator or an administrator. We want to take a select few tags to be set to the main alarm page and make a new alarm page for a sub-operator to e able to clear these few alarms. or add another acknowledged to the main alarm screen that will only clear these few alarms. So if the sub-operator Ack. the select alarms they clear for both or if the main operator clears it also clears them alarms and of course the other alarms. Is there a way to do this. Thank you in advance for the help.

Note: Ignition Version is 7.5.11

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 9, 2022, 1:58pm UTC](https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543/2 "2022-06-09T13:58:15Z")

</div>

Hmm. There’s no online docs for v7.5 and I haven’t run one (with local docs) in ages.

Since v7.8 per the docs, there are script functions that can acknowledge specific alarms. That could be used in a script that looks at the current list of active alarms and acknowledges just the ones that meet your subset criteria.

Look for something similar in your v7.5 docs.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [June 9, 2022, 3:28pm UTC](https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543/3 "2022-06-09T15:28:49Z")

</div>

I think 7.5 might be old enough it’s got “alerts”, not alarming. All bets are off.

---

<div class="post-metadata">

**Author:** ![Chase\_Viche](https://avatars.discourse-cdn.com/v4/letter/c/e5b9ba/32.png) [@Chase\_Viche](https://forum.inductiveautomation.com/u/Chase_Viche)\
**Post date:** [June 9, 2022, 9:08pm UTC](https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543/4 "2022-06-09T21:08:26Z")

</div>

That is correct, it is alerting in 7.5. Any dance around you could think of.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [June 9, 2022, 9:18pm UTC](https://forum.inductiveautomation.com/t/need-some-help-advice-on-alarming/60543/5 "2022-06-09T21:18:26Z")

</div>

If you download a zip installer for 7.5.X, you can get the ‘User Manual Module’ that it includes. The manual module can be opened by an archive utility, then the `help.jar` file can be opened again by an archive utility, and then you can browse the `doc` folder contained therein. I’d upload it here directly, but it’s too big for our forum software to allow.

Here’s the two most relevant `system.alert` system functions - that may be enough to be helpful.  
[Archive.zip](https://forum.inductiveautomation.com/uploads/short-url/exygo3xuyFrD7oc9aUmy3SY0Vz0.zip) (6.0 KB)