# Need to create a tag in Hexadecimal

**URL:** <https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208>\
**Category:** Ignition\
**Created:** [December 4, 2018, 2:32pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208 "2018-12-04T14:32:53Z")\
**Posts on this page:** 12\
**Page:** 1

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 4, 2018, 2:32pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/1 "2018-12-04T14:32:53Z")

</div>

I have a modbus device that contains 12 tags according to the diagnistics of the device. The addressing are in Hexadecimal that are working on Kepware. We are trying to put this in Ignition but the address is H417FF and the limit is 0-65535 which my value is out of range 267000 something like that. How do we configure the address of this device?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 4, 2018, 3:00pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/2 "2018-12-04T15:00:51Z")

</div>

Try omitting the leading “4”.

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 4, 2018, 3:32pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/3 "2018-12-04T15:32:39Z")

</div>

I tried that and still add to convert the remaining 4 char from Hex to Dec which is a valid number. Used the radix 16, not sure exactly what is the radix (is this for adress or the number of tags).

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 5, 2018, 3:45pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/4 "2018-12-05T15:45:11Z")

</div>

Any news on how to read a modbus device that has its addresses in Hexadecimal which is out of range of the 65535?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 5, 2018, 4:03pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/5 "2018-12-05T16:03:07Z")

</div>

Generally, in modbus, the leading “4” is a type indicator, not really part of the address. Without the “4”, your hexadecimal address is well within the 16-bit range. Please identify the device and/or share the datasheet with the addresses of interest.

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 5, 2018, 4:24pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/6 "2018-12-05T16:24:54Z")

</div>

![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/8d000812f7045feb12c4a440351cc6112f098df7.png)Tag Name Address  
INV\_AC\_POW H417FF  
INV\_FAULT\_CODE H41806  
INV\_PPT\_MAX H4FA04  
INV\_PV\_CURRENT H41801  
INV\_PV\_POW H41802  
INV\_PV\_VOLT H41800  
INV\_STATE H41804

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 5, 2018, 4:33pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/7 "2018-12-05T16:33:02Z")

</div>

So these would be in Ignition, [per the manual](https://docs.inductiveautomation.com/display/DOC79/Modbus+Addressing):

- INV\_AC\_POW = HR6143
- INV\_FAULT\_CODE = HR6150
- INV\_PPT\_MAX = HR64004
- INV\_PV\_CURRENT = HR6145
- INV\_PV\_POW = HR6146
- INV\_PV\_VOLT = HR6144
- INV\_STATE = HR6148

Some devices might need zero-based addressing instead of one-based addressing, in Ignition’s device setup.

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 5, 2018, 4:43pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/8 "2018-12-05T16:43:17Z")

</div>

> [@pturmel](#):
>
> HR6143

Tried two tags with two devices, the flag Zero based is different with each other, no results

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 5, 2018, 4:46pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/9 "2018-12-05T16:46:47Z")

</div>

Sounds like you need support looking over your shoulder, or perhaps collecting network traffic to compare Kepware vs. Ignition.

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 5, 2018, 4:49pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/10 "2018-12-05T16:49:20Z")

</div>

Working remote for these plants is not easy to implement a sniffer.  
Just checked the invoices for my last 4 licences and yep, we have full phone support.  
Thought I used the forum first.

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 6, 2018, 6:44pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/11 "2018-12-06T18:44:37Z")

</div>

Somehow, it actually work with the software Modbus Poll.  
I have setup one tag with the right address : 6143 and it returns a valid value.

However, still unable to set that up into Ignition.  
Called support, I should have a call back within 10-15 minutes.

---

<div class="post-metadata">

**Author:** ![patrick.garceau](https://avatars.discourse-cdn.com/v4/letter/p/76d3ee/32.png) [@patrick.garceau](https://forum.inductiveautomation.com/u/patrick.garceau)\
**Post date:** [December 6, 2018, 8:53pm UTC](https://forum.inductiveautomation.com/t/need-to-create-a-tag-in-hexadecimal/21208/12 "2018-12-06T20:53:15Z")

</div>

So gfot to support and the tag is actually : 1.HR6143  
So that works now.

Thanks everyone.