> [@Curiosity? Gateway Timer Event Scripts](https://forum.inductiveautomation.com/t/curiosity-gateway-timer-event-scripts/102368/9):
>
> As Ryan suggests, don't count in a timer event. The timing is not very precise. To get retention of prior time, you need at least two timestamps to hold state, updated when the signal changes. A stop timestamp, and an adjusted start timestamp. The start timestamp needs to be adjusted backwards from now() by the amount accumulated before. Drop these tags into a test folder to see how to set this up: { "tags": [{ "valueSource": "expr", "expression": "if(\n\t{[.]RTO\_Reset},…

---