# New DNP3 Module Read After Operate Not Working?

**URL:** <https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157>\
**Category:** Ignition\
**Created:** [March 11, 2024, 8:31pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157 "2024-03-11T20:31:08Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![edward.fowler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/edward.fowler/32/24179_2.png) [@edward.fowler](https://forum.inductiveautomation.com/u/edward.fowler)\
**Post date:** [March 11, 2024, 8:31pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/1 "2024-03-11T20:31:08Z")

</div>

I'm not saying this setting isn't working, but I thought it would fix the issue.

The issue is the value of my DNP3 analog output tag is always _one behind_.

I have a test tag (memory) with a value changed script that writes the value to a DNP3 analog output (OPC item path) tag each time the test tag value changes. The value of the DNP3 analog output tag always shows the previous value. I know the output is working because I'm monitoring the address in the RTAC, it shows the same value as the test tag (so I know the output is working).

Here's a little sequence if my previous explanation is poor.

```auto
test tag value: 1, 2, 3, 4, 5, 6, 7, 8
DNP analog output tag: 1, 2, 3, 4, 5, 6, 7
RTAC tag: 1, 2, 3, 4, 5, 6, 7, 8

```

The device configuration includes:  
Command Mode - DIRECT\_OPERATE  
Read After Operation - TRUE

Is there something I'm missing in my configuration?

Side note - this doesn't happen with the Legacy DNP3 driver and the same RTAC.

Ignition v8.1.37  
New DNP3 Module v1.1.38.2024030513

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 11, 2024, 8:33pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/2 "2024-03-11T20:33:16Z")

</div>

Wireshark capture?

Maybe the RTU takes a little too long to execute and the read-after-operate ends up reading the old value. 8.1.39 has a new setting to insert a configurable delay before the read-after-operate is issued.

---

<div class="post-metadata">

**Author:** ![edward.fowler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/edward.fowler/32/24179_2.png) [@edward.fowler](https://forum.inductiveautomation.com/u/edward.fowler)\
**Post date:** [March 11, 2024, 9:11pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/3 "2024-03-11T21:11:09Z")

</div>

I can't share the packet capture (need to keep the IPs hidden), but here are some screen shots. Apologies if its hard to follow.

@Kevin.Herron It looks like you nailed it.  
What delay does the legacy driver use?  
When will 8.1.39 be released?  
The RTAC is an SEL-3505. Not an expert on this but I'll look for some settings.  
Thanks Kevin.

* * *

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/0/4022c4a19df7d7c408bcee39265f3b5af535a96d.png)

* * *

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/5/257056e616848ef0016b482609173ee2ca2fa4ab.png)

* * *

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/e/fe784f67d78a1492eb511d5e99802850d8276a18.png)

* * *

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/f/7f3ce056803c2fcada54a95bd4bfc93562278912.png)

* * *

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/a/eaad8de98700310491693eb0ca1e0e0661483a93.png)

* * *

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 11, 2024, 9:22pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/4 "2024-03-11T21:22:26Z")

</div>

The legacy driver doesn't issue an explicit read-after-operate, but it was probably explicitly polling that point as a consequence of how the legacy driver operated, so you eventually saw the update.

The new driver is using class-based polling by default, and read-after-operate is a hack for outstations that don't generate an analog output event with the new value after the operation completes.

---

<div class="post-metadata">

**Author:** ![Mark\_Phillips](https://avatars.discourse-cdn.com/v4/letter/m/73ab20/32.png) [@Mark\_Phillips](https://forum.inductiveautomation.com/u/Mark_Phillips)\
**Post date:** [April 2, 2024, 10:14pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/5 "2024-04-02T22:14:44Z")

</div>

Kevin, when is 8.1.39 scheduled to be released? I am having the same issue.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [April 2, 2024, 10:35pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/6 "2024-04-02T22:35:31Z")

</div>

As soon as April 9th, though no sooner.

---

<div class="post-metadata">

**Author:** ![Mark\_Phillips](https://avatars.discourse-cdn.com/v4/letter/m/73ab20/32.png) [@Mark\_Phillips](https://forum.inductiveautomation.com/u/Mark_Phillips)\
**Post date:** [April 9, 2024, 9:00pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/7 "2024-04-09T21:00:22Z")

</div>

Thanks! I am excited to test it out.

---

<div class="post-metadata">

**Author:** ![Mark\_Phillips](https://avatars.discourse-cdn.com/v4/letter/m/73ab20/32.png) [@Mark\_Phillips](https://forum.inductiveautomation.com/u/Mark_Phillips)\
**Post date:** [April 12, 2024, 4:47pm UTC](https://forum.inductiveautomation.com/t/new-dnp3-module-read-after-operate-not-working/87157/8 "2024-04-12T16:47:14Z")

</div>

Thanks! I set the "Read After Operate Delay (ms)" to 1000 ms for the analog output point and it's working well.