Nightly Changelog: 8.1.43-SNAPSHOT-b20240724

## Swing

### Designer

**IGN-10047: Disabled user source causes errors in Designer project properties**  
Fixed an issue in the Project Properties Panel where roles were being retrieved for unselected User Sources, causing an error popup when the panel was opened if the user source was disabled.

## Foundation

### Installers

**IGN-10368: remove launch-homepage.bat file (backport)**  
the broken launch-homepage batch file is removed from windows installs  
**IGN-7643: Windows: When upgrading from 7.9 to 8.1 using the ZIP installer, the run-upgrader.bat file doesn’t complete successfully when clicking in Explorer**  
The Windows run-upgrader.bat file and gwcmd.bat file have been fixed with improved handling for prompting authorization via UAC when run by a non-privileged user if the installation requires elevated privileges.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [July 26, 2024, 7:27am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/119 "2024-07-26T07:27:46Z")

</div>

Nightly Changelog: 8.1.43-SNAPSHOT-b20240725

## Perspective

### Perspective

**IGN-10299: Alarm Status Table: ‘Event Time’ format in alarm details will ignore dateFormat property when the source tag clears the alarm**  
Fixed an issue in the Alarm Status Table that caused an alarm's displayed event time to ignore the configured dateFormat property.  
**IGN-10253: Alarm Status Table ‘Event Time’ in alarm details will add time as alarm triggers/clears with certain timezoneId values**  
Fixed an issue in the Alarm Status Table that caused an alarm's displayed event time to be incorrectly timezone adjusted.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [August 1, 2024, 7:27am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/120 "2024-08-01T07:27:59Z")

</div>

Nightly Changelog: 8.1.43-SNAPSHOT-b20240731

## Foundation

### Launchers

**IGN-10460: The Vision Client Launcher will try to connect to the backup gateway on a non-SSL address if the master is using SSL and force secure redirect is not enabled (backport to 8.1)**  
Vision Client Launcher now assumes the same protocol for backup gateways as the protocol used when connecting to the master, preventing potential insecure connection downgrades when launching against a redundant pairs when the backup is active and the master is down.

## Alarming

### Voice Notification

**IGN-10073: Voice Notification Profile NPE**  
Fixed a NPE that would occur if the call receiver hung up before the voice notification finished the script

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [August 2, 2024, 7:27am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/121 "2024-08-02T07:27:05Z")

</div>

Nightly Changelog: 8.1.43-SNAPSHOT-b20240801

## Alarming

### Alarm Notification

**IGN-10118: Email Alarm Notification Consolidation no longer working in 8.1.39**  
Fixed a regression which prevented alarm notification consolidation from working properly.

## Tag Historian

### Tag Historian

**IGN-8203: Tag History: When unable to create a new partition in the database or insert into the sqlth\_partitions table, all subsequent historical data that would be inserted into that partition is dropped instead of quarantined**  
Fixed an issue where store and forward data was being dropped when the database user didn't have privileges to create tables or insert data. Now, this data is stored into quarantine.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [August 3, 2024, 7:25am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/122 "2024-08-03T07:25:13Z")

</div>

Nightly Changelog: 8.1.43-SNAPSHOT-b20240802

## Platform Core

### Licensing

**IGN-10217: Display Banner for Development Licenses - 8.1 Gateway**  
A banner will now be displayed on the gateway web interface pages when a _development_ license for Ignition is active.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [August 15, 2024, 7:21am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/123 "2024-08-15T07:21:26Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240814

## Perspective

### Perspective

**IGN-9264: Alarm Journal and Status Table: capital letters in associated data names create extra spaces in the alarm details**  
Fixed an issue that resulted in Associated Data keys being converted to title case when viewing alarm details from Perspective Alarm Journal and Status Tables.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [August 28, 2024, 7:21am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/125 "2024-08-28T07:21:10Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240827

## Alarming

### Alarm Status

**IGN-10098: Ack User and Ack Notes of the Alarm Status Table go blank after alarm is cleared**  
Fixed an issue where an alarm event's ack user and ack notes would stop displaying in Alarm Status Table components' columns after the alarm was Cleared

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [August 30, 2024, 7:27am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/127 "2024-08-30T07:27:28Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240829

## Comms

### Drivers

**IGN-10743: Many BACnet device connections can cause slow writes**  
Fixed an issue where a significant number of BACnet remote device connections could cause write requests to send out slower than expected.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [September 13, 2024, 7:21am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/134 "2024-09-13T07:21:45Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240912

## Security

### Security

**IGN-10385: Security: tag permissions affect reads/writes on Value Changed scripts when triggered by Perspective event**  
Fixed an issue where tag event scripts triggered from Perspective would incorrectly inherit the security context of the Perspective session. This could prevent tag event scripts from working as intended due to insufficient permissions.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [September 17, 2024, 7:21am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/136 "2024-09-17T07:21:46Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240916

## Tags

### Tags & UDTs

**IGN-10498: UDT: Parameter offsets evaluate to null when parameter name begins with an integer**  
Fixed issue where parameter names with leading integer values were failing to evaluate in UDT bindings

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [September 21, 2024, 7:22am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/140 "2024-09-21T07:22:04Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240920

## Tags

### Tags & UDTs

**IGN-10836: Backport: Dragging and dropping folders allows folders to be inserted into themselves**  
Resolved an issue where moving folders on themselves within the Tag Browser could cause the folder to be deleted

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [September 26, 2024, 7:21am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/143 "2024-09-26T07:21:10Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240925

## Security

### Security

**IGN-10238: Backport: Upgrade Bouncy Castle**  
Upgraded bouncy castle library from 1.69 to 1.78.1

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [September 28, 2024, 7:22am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/145 "2024-09-28T07:22:58Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240927

## Security

### Security

**IGN-10910: A Null Pointer Exception is thrown when Domain property in an AD user source is blank**  
Fixed a Null Pointer Exception that occurred if the domain property was left blank when configuring Active Directory User Sources.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [October 1, 2024, 7:20am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/146 "2024-10-01T07:20:52Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20240930

## Foundation

### Launchers

**IGN-10027: Designer silently fails to launch if a Screen Reader has been installed on Windows**  
Fixed a compatibility issue with Ignition Designer when certain screen readers are installed.

## Comms

### Drivers

**IGN-10455: Mitsubishi driver: ZR area cannot be accessed on Q/L series**  
Fixed an issue where ZR registers were inaccessible on Mitsubishi Q/L series devices.

## Infrastructure

### Java - Azul

**IGN-9701: Investigate necessity of classes.jsa in 8.1.33+**  
Fixed an issue where an upgrade could fail during Ignition runtime file extraction.  
**IGN-10360: Bump bundled java runtime to 17.0.12**  
Upgraded the Java Runtime Environment (JRE) version to 17.0.12.

## Perspective

### Perspective

**IGN-9290: Opening a Perspective view in the Designer results in the view not rendering properly at random.**  
Fixed a race condition that could result in views failing to load in the Designer.

## Alarming

### Alarm Status

**IGN-10294: isShelved Property Remains True Post-Shelving Period When Using alarmPath Parameter in system.alarm.shelve() Function**  
Fixed an issue where an alarm's isShelved property could remain true after the shelving period expires.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [October 2, 2024, 7:20am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/147 "2024-10-02T07:20:27Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20241001

## Swing

### Vision

**IGN-10926: Support document datatype in Vision custom properties**  
Added support for the 'Document' data type in Vision custom properties.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [October 4, 2024, 7:22am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/149 "2024-10-04T07:22:21Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20241003

## Swing

### Vision

\*\*IGN-10702: Vision Week View component tool tip displays the incorrect date range when events span multiple days \*\*  
Fixes the tooltip's date range in the Week View component when displaying multi-day events  
**IGN-9513: Vision SVGs are not perfectly Snapping to Grid with Int values when not at 100% zoom**  
Fixes issue where snap to grid did not snap to integer values

### Designer

**IGN-9599: Unable to click and edit property field when respective Designer Tooltip display is active**  
Fixed some nuisance tooltips in certain property editors obscuring content before you could interact with it. Also offset the Script Console's 'Execute' button tooltip to prevent it overlapping the button when the console window is maximized.

## Perspective

### Perspective

**IGN-2602: Workstation on screen keyboard: input focus change inconsistent with chromium**  
Multiple issues with the On Screen Keyboard have been addressed including focus and the keyboard displaying correctly on top of the browser window.  
**IGN-7032: Perspective Workstation: Launching a Second Display has a Long Load Time**  
Using multiple monitors in Perspective Workstation now has a faster response time when starting to load pages on secondary monitors.  
**IGN-2605: Workstation on screen keyboard: spellchecker holds focus permanently, preventing interaction**  
The On Screen Keyboard in Perspective Workstation now works with spellchecker being enabled on Windows.  
**IGN-2604: Workstation on screen keyboard: dropdown selection**  
Dropdown selection when using an On Screen Keyboard in Perspective Workstation with search enabled now allows selection of the elements in the drop down.  
**IGN-7584: Workstation: upgrade JxBrowser dependency to more recent version**  
Upgrades JXBrowser for Workstation to 7.40.0 which includes chromium 127.0.6533.73. Also swaps the implementation to use Swing instead of JavaFX for a more consistent experience along with a lot of bug fixes.

### Workstation

**IGN-7583: Perspective Workstation on Red Hat Enterprise Linux (RHEL) opens small windows in Kiosk mode.**  
Perspective Workstation Kiosk mode on Red Hat Enterprise Linux now opens full screen on the target monitor instead of as a small window.  
**IGN-8487: Refactor Workstation's Browser Window to use Swing instead of JavaFX**  
Perspective Workstation has swapped its implementation from JavaFX to Swing for the embedded browser views for a more consistent and reliable experience. This will also improve the our ability to upgrade the embedded version of chromium more frequently in the future.

## Containers

### Cloud Edition

**IGN-10913: Bump the bundled version of Cirrus Link modules to 4.0.24**  
Updated Ignition Cloud Edition bundled Cirrus Link MQTT modules to version 4.0.24.

---

<div class="post-metadata">

**Author:** ![Wyatt\_Dias](https://avatars.discourse-cdn.com/v4/letter/w/e0b2c6/32.png) [@Wyatt\_Dias](https://forum.inductiveautomation.com/u/Wyatt_Dias)\
**Post date:** [October 4, 2024, 5:11pm UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/150 "2024-10-04T17:11:13Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20241003

## Perspective

### Perspective

**IGN-2603: Workstation on screen keyboard: input selection doesn't bring the selected component into view**  
Perspective Workstation now keeps the target component visible when using the On Screen Keyboard.

---

<div class="post-metadata">

**Author:** ![Wyatt\_Dias](https://avatars.discourse-cdn.com/v4/letter/w/e0b2c6/32.png) [@Wyatt\_Dias](https://forum.inductiveautomation.com/u/Wyatt_Dias)\
**Post date:** [October 7, 2024, 5:06pm UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/151 "2024-10-07T17:06:47Z")

</div>

Nightly Changelog: 8.1.44-SNAPSHOT-b20241001

## Perspective

### Perspective

**IGN-10944: Backport: Update axios to version 2.8+ for CVE with score of 7.1**  
Resolved identified security vulnerability BDSA-2023-2855.

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [October 19, 2024, 7:26am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/152 "2024-10-19T07:26:55Z")

</div>

Nightly Changelog: 8.1.45-SNAPSHOT-b20241018

## Tags

### Tags & UDTs

**IGN-9514: Errors in Tag Change Scripts can be hard to identify after first error is thrown**  
If an error occurs with a tags Value Change script it only logged once unless a specific logger was in debug mode, it will now be noted in the logs once per minute

---

<div class="post-metadata">

**Author:** ![system](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c985ea71ed53a8f212f3920ddf03fe05249170b8.png) [@system](https://forum.inductiveautomation.com/u/system)\
**Post date:** [October 23, 2024, 7:22am UTC](https://forum.inductiveautomation.com/t/nightly-8-1-changelogs-2024/83608/153 "2024-10-23T07:22:29Z")

</div>

Nightly Changelog: 8.1.45-SNAPSHOT-b20241022

## Perspective

### Perspective

**IGN-10930: Geolocation fails to retrieve data on recent desktop browser versions**  
Geolocation functionality in Perspective now works with the most recent version of multiple browsers on desktop, including Google Chrome, Microsoft Edge, and Firefox. In particular, on Firefox version 130 and Chromium versions 126 and above.