I’m passing some data from an SQL database to Ignition and then to a PLC. The number in the database is 3 digits and the PLC needs to see the same 3 digits. I would like ignition to display the number /100. Is there an easy way to accomplish this?

SQL value = 834  
PLC receives 834  
Ignition Displays 8.34

---

<div class="post-metadata">

**Author:** ![Paul.Scott](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul.scott/32/4578_2.png) [@Paul.Scott](https://forum.inductiveautomation.com/u/Paul.Scott)\
**Post date:** [June 20, 2014, 4:45pm UTC](https://forum.inductiveautomation.com/t/numeric-display/8597/2 "2014-06-20T16:45:00Z")

</div>

You can use an Expression binding on the Value property of your component. Try this:

```auto
{Tag/Path}/100
```

This would show the quotient on your component, but wouldn’t change the value that PLC receives.

---

<div class="post-metadata">

**Author:** ![diat150](https://avatars.discourse-cdn.com/v4/letter/d/a587f6/32.png) [@diat150](https://forum.inductiveautomation.com/u/diat150)\
**Post date:** [June 20, 2014, 6:34pm UTC](https://forum.inductiveautomation.com/t/numeric-display/8597/3 "2014-06-20T18:34:23Z")

</div>

you can also set up linear scaling on your tag. something like raw max = 10000 scaled max = 100