# Omron CJ2M CPU33

**URL:** <https://forum.inductiveautomation.com/t/omron-cj2m-cpu33/70424>\
**Category:** Ignition\
**Created:** [February 28, 2023, 3:18pm UTC](https://forum.inductiveautomation.com/t/omron-cj2m-cpu33/70424 "2023-02-28T15:18:02Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![Alfredo\_Egmo](https://avatars.discourse-cdn.com/v4/letter/a/ccd318/32.png) [@Alfredo\_Egmo](https://forum.inductiveautomation.com/u/Alfredo_Egmo)\
**Post date:** [February 28, 2023, 3:18pm UTC](https://forum.inductiveautomation.com/t/omron-cj2m-cpu33/70424/1 "2023-02-28T15:18:02Z")

</div>

I am having issues to configure OMRON tags  
This is what I have configured with no sucess  
as I understand for OMRON I have to configure the tags under the GATEWAY first and then under the designer..  
Any help welcome.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/2/02f7950cd76a4c695e3bc7905424136f439fb8e0.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 28, 2023, 4:27pm UTC](https://forum.inductiveautomation.com/t/omron-cj2m-cpu33/70424/2 "2023-02-28T16:27:34Z")

</div>

The tag configuration in the gateway is optional, it just makes them browsable, but you can also create tags manually and just specify the address.

I'm not sure if `D05026` is valid or not. Can you try without the leading 0? If that doesn't work there may be some logging to try.

---

<div class="post-metadata">

**Author:** ![Alfredo\_Egmo](https://avatars.discourse-cdn.com/v4/letter/a/ccd318/32.png) [@Alfredo\_Egmo](https://forum.inductiveautomation.com/u/Alfredo_Egmo)\
**Post date:** [February 28, 2023, 5:01pm UTC](https://forum.inductiveautomation.com/t/omron-cj2m-cpu33/70424/3 "2023-02-28T17:01:45Z")

</div>

thanks, that's a valid address, I can see it in the PLC software, I tried with no leading zero D5026 and DM5026 with no sucess.  
I reviewed the log here , but I don't see anything related to that tag/plc, do I have to look in other place other way to check this issue events?

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/b/3b7adf32961b717637d22c7beb364dbf5ab51057.png)

---

<div class="post-metadata">

**Author:** ![Alfredo\_Egmo](https://avatars.discourse-cdn.com/v4/letter/a/ccd318/32.png) [@Alfredo\_Egmo](https://forum.inductiveautomation.com/u/Alfredo_Egmo)\
**Post date:** [February 28, 2023, 9:40pm UTC](https://forum.inductiveautomation.com/t/omron-cj2m-cpu33/70424/4 "2023-02-28T21:40:23Z")

</div>

I found the issue, I was assigning DESTINATION NODE in the Gateway., Once I put it in 0 it works  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/1/0178edcbf73fb974d8f5f6728c8fdd70b6bdb933.png)