hi, i am facing the below issue.

i have connected 20 Omron FINS devices in ignition gateway and total of 134 other device configuration.  
i am facing frequent reconnectwait issue . some of the devices are connected and some are showing reconnectWait issue.  
In logs i found the following error.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/3/c3fb20d9b746952f01db50d1a7af93e6ff848f50.jpeg)

Any solution for this would be appreciated.

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [September 20, 2024, 10:30am UTC](https://forum.inductiveautomation.com/t/omron-fins-plc-reconnectwait/96217/2 "2024-09-20T10:30:48Z")

</div>

You may find this thread of interest.

> [@Edge 8.1.7 with OPC UA Omron FINS/TCP connection experiencing overloading and slow read](https://forum.inductiveautomation.com/t/edge-8-1-7-with-opc-ua-omron-fins-tcp-connection-experiencing-overloading-and-slow-read/60167):
>
> Hi All, I’m using edge 8.1.7 with OPC UA Omron FINS/TCP connection. On the Status\>Connections\>Devices page, it shows overloading of PLC. The write/sending of values to the plc is instantaneous, but the reading from PLC to gateway is slow. Having delay of 3-6++ seconds. While reading the OMRON FINS Driver manual, it mentioned about FINS Settings and Request Optimization. For FINS Settings, right now all the values are default:0 in the configuration. But on the actual PLC, we have tuned the…

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 20, 2024, 1:28pm UTC](https://forum.inductiveautomation.com/t/omron-fins-plc-reconnectwait/96217/3 "2024-09-20T13:28:21Z")

</div>

Can you get and share a Wireshark capture?

Are you setting "Source Node" to something other than 0 for your devices?

---

<div class="post-metadata">

**Author:** ![vani161998](https://avatars.discourse-cdn.com/v4/letter/v/ee7513/32.png) [@vani161998](https://forum.inductiveautomation.com/u/vani161998)\
**Post date:** [September 24, 2024, 4:37am UTC](https://forum.inductiveautomation.com/t/omron-fins-plc-reconnectwait/96217/4 "2024-09-24T04:37:52Z")

</div>

Source node is Ignition Last two IP number  
Destination node is PLC last two IP number