# Omron PLC to Ignition

**URL:** <https://forum.inductiveautomation.com/t/omron-plc-to-ignition/96209>\
**Category:** Ignition\
**Tags:** perspective\
**Created:** [September 19, 2024, 10:12pm UTC](https://forum.inductiveautomation.com/t/omron-plc-to-ignition/96209 "2024-09-19T22:12:14Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![Iman\_Khamo](https://avatars.discourse-cdn.com/v4/letter/i/50afbb/32.png) [@Iman\_Khamo](https://forum.inductiveautomation.com/u/Iman_Khamo)\
**Post date:** [September 19, 2024, 10:12pm UTC](https://forum.inductiveautomation.com/t/omron-plc-to-ignition/96209/1 "2024-09-19T22:12:14Z")

</div>

Ignition connection to Omron fins , Unable to connect,  
Citect is able to connect however ignition struggles.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/b/5b93968cfa3cbcb622e91a075c1aa496baf1c81b.jpeg)

I've tried multiple method even NJ drivers which connects but doesn't get values from tags.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/6/2659e388ed83c6abc2369e03ee8090ba5546dc7c.png)

Let me know if you guys can help.

---

<div class="post-metadata">

**Author:** ![simeonw](https://avatars.discourse-cdn.com/v4/letter/s/4da419/32.png) [@simeonw](https://forum.inductiveautomation.com/u/simeonw)\
**Post date:** [September 20, 2024, 1:12am UTC](https://forum.inductiveautomation.com/t/omron-plc-to-ignition/96209/2 "2024-09-20T01:12:08Z")

</div>

It is difficult to see why your Ignition driver or address configurations aren't working if we can't see them. Please could you include a screenshot of your NJ Addressing configuration and the FINS driver configuration.

If you are having issues with the NJ tags values not updating, you may need to double check how you are addressing your data points:

[Omron NJ Driver | Ignition User Manual (inductiveautomation.com)](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/omron-nj-driver)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 20, 2024, 5:48pm UTC](https://forum.inductiveautomation.com/t/omron-plc-to-ignition/96209/3 "2024-09-20T17:48:52Z")

</div>

Also be aware that IA's NJ/NX driver does **not** browse the tags in the target PLC. You must export from Sysmac Studio and import into IA's device configuration. If you'd like a better experience with NJ/NX PLCs, you probably want to use my alternate EtherNet/IP Client driver:

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190):
>
> Automation Professionals is pleased to announce its latest EtherNet/IP Communications Suite driver module, a major upgrade to its EtherNet/IP Class1 Communications module, as a Public Beta. As of April 15, 2023, this is now a Production Release. The primary new feature is its new Generic EtherNet/IP Client Driver, a drop-in replacement for IA's Logix V21+ driver and its Omron NJ/NX driver. It does work with older Logix processors, and also works with Rockwell's MicroLogix 8xx family (ethernet…

(Dramatic performance increase, too.)