Also be aware that IA's NJ/NX driver does **not** browse the tags in the target PLC. You must export from Sysmac Studio and import into IA's device configuration. If you'd like a better experience with NJ/NX PLCs, you probably want to use my alternate EtherNet/IP Client driver:

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190):
>
> Automation Professionals is pleased to announce its latest EtherNet/IP Communications Suite driver module, a major upgrade to its EtherNet/IP Class1 Communications module, as a Public Beta. As of April 15, 2023, this is now a Production Release. The primary new feature is its new Generic EtherNet/IP Client Driver, a drop-in replacement for IA's Logix V21+ driver and its Omron NJ/NX driver. It does work with older Logix processors, and also works with Rockwell's MicroLogix 8xx family (ethernet…

(Dramatic performance increase, too.)

---