I need to connect to a checkweigher device that has an OPC-UA server module gateway unit that data can be extracted from. In preparation for when this device is installed, I am looking at the device connection options in Ignition. My assumption is that I would use the OPC-COM Tunnel Driver to connect Ignition to this OPC-UA unit to collect the data. But I wasn't sure if I was understanding if that is what this tunnel driver is for? Please advise.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 16, 2024, 2:06pm UTC](https://forum.inductiveautomation.com/t/opc-com-tunnel-driver/85837/2 "2024-02-16T14:06:43Z")

</div>

No, if your device has an OPC UA server, then you just make an OPC UA connection to it. No tunnel driver involved.

> **[OPC UA Client Connection Settings | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-client-connection-settings#configuring-an-opc-client-connection)**
>
> Configuring an OPC Client Connection