Hi…

Yet another way to pair Ignition with RSLogix Emulate 5000 is: Ignition \> OPC-DA \> FactoryTalk Gateway \> RSlinx Enterprise.

\*EDIT: **_FactoryTalk Gateway must be installed prior to attempting this method._**

1. In **FactoryTalk Administrator** set up a new **local** application with an **RSLinx Enterprise Server** and a new shortcut pointing to the emulator.
2. In **Ignition Gateway** create a new **OPC Server Connection**.  
• Choose **OPC-DA COM Connection** ;[next] **Local** ; [next] **FactoryTalk Gateway**  
• Name it the **same** as the shortcut in step 1  
• Save changes.
3. Start emulator, download code, put in run.
4. Open **Ignition Designer** and refresh the OPC Browser. Your connection should show up with all the tags live from the emulator.

As you were,  
Steve

---