# OPC Item path for an array tag

**URL:** <https://forum.inductiveautomation.com/t/opc-item-path-for-an-array-tag/89037>\
**Category:** Ignition\
**Created:** [April 18, 2024, 12:41pm UTC](https://forum.inductiveautomation.com/t/opc-item-path-for-an-array-tag/89037 "2024-04-18T12:41:14Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Giacomo\_Saccani](https://avatars.discourse-cdn.com/v4/letter/g/e99b99/32.png) [@Giacomo\_Saccani](https://forum.inductiveautomation.com/u/Giacomo_Saccani)\
**Post date:** [April 18, 2024, 12:41pm UTC](https://forum.inductiveautomation.com/t/opc-item-path-for-an-array-tag/89037/1 "2024-04-18T12:41:14Z")

</div>

Hello

I am trying to define the OPC item path for an array tag with an S7-1200, however I can't seem to figure out what is the correct syntax and if that is even possible.  
The PLC tag is stored in a DB without optimized access and it is composed of 120 DInt elements.

Thank you

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 18, 2024, 12:44pm UTC](https://forum.inductiveautomation.com/t/opc-item-path-for-an-array-tag/89037/2 "2024-04-18T12:44:53Z")

</div>

IIRC, IA's native driver won't bring in an array into a single tag.