> [@Kevin.Herron](#):
>
> just not using the Modbus address map at all

💯 I heartily endorse this opinion.

Related topic:

> [@How to create multiple similar Modbus TCP devices including registers?](https://forum.inductiveautomation.com/t/how-to-create-multiple-similar-modbus-tcp-devices-including-registers/52287/12):
>
> If browsability is important, you might consider my [Advanced Modbus Driver](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-advanced-modbus). No mapping needed. Configuration required if not using the default node address, though (1).

---