# OPC server connection Keep-Alive Failures Allowed and Failover Threshold

**URL:** <https://forum.inductiveautomation.com/t/opc-server-connection-keep-alive-failures-allowed-and-failover-threshold/20990>\
**Category:** Ignition\
**Tags:** ignition79\
**Created:** [November 21, 2018, 7:59am UTC](https://forum.inductiveautomation.com/t/opc-server-connection-keep-alive-failures-allowed-and-failover-threshold/20990 "2018-11-21T07:59:19Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![mik977](https://avatars.discourse-cdn.com/v4/letter/m/5f8ce5/32.png) [@mik977](https://forum.inductiveautomation.com/u/mik977)\
**Post date:** [November 21, 2018, 7:59am UTC](https://forum.inductiveautomation.com/t/opc-server-connection-keep-alive-failures-allowed-and-failover-threshold/20990/1 "2018-11-21T07:59:19Z")

</div>

How are the Keep-Alive Failures Allowed and Failover Threshold related with respect to disconnect event due to Keep-Alive Failures Allowed beeing 1,2,… or 0?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 21, 2018, 2:05pm UTC](https://forum.inductiveautomation.com/t/opc-server-connection-keep-alive-failures-allowed-and-failover-threshold/20990/2 "2018-11-21T14:05:47Z")

</div>

They aren’t really related to each other.