# OPC server connection status faulted

**URL:** <https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730>\
**Category:** Ignition\
**Created:** [May 7, 2019, 8:36am UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730 "2019-05-07T08:36:37Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![maohanwen1017](https://avatars.discourse-cdn.com/v4/letter/m/9d8465/32.png) [@maohanwen1017](https://forum.inductiveautomation.com/u/maohanwen1017)\
**Post date:** [May 7, 2019, 8:36am UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730/1 "2019-05-07T08:36:37Z")

</div>

Hello, I’m trying to use ignition to connection with wago 750-8212 controller, but after add the address of the controller at opc connection on Ignition, the status shows faulted, what did I do wrongly?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 7, 2019, 12:12pm UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730/2 "2019-05-07T12:12:47Z")

</div>

What version of Ignition are you using?

There should be an error message with a fault reason on the status page, what’s it say?

---

<div class="post-metadata">

**Author:** ![maohanwen1017](https://avatars.discourse-cdn.com/v4/letter/m/9d8465/32.png) [@maohanwen1017](https://forum.inductiveautomation.com/u/maohanwen1017)\
**Post date:** [May 8, 2019, 1:25am UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730/3 "2019-05-08T01:25:45Z")

</div>

Hi, thanks for your reply, I’m using version 8.0.0.

The message shown is here :UaException: status=Bad\_Timeout, message=io.netty.channel.ConnectTimeoutException: connection timed out: /192.168.1.2:4840  
at org.eclipse.milo.opcua.stack.client.transport.uasc.ClientChannelFsm$ClientChannelActions.lambda$connect$0(ClientChannelFsm.java:124)  
at io.netty.util.concurrent.DefaultPromise.notifyListener0(DefaultPromise.java:502)  
at io.netty.util.concurrent.DefaultPromise.notifyListeners0(DefaultPromise.java:495)  
at io.netty.util.concurrent.DefaultPromise.notifyListenersNow(DefaultPromise.java:474)  
at io.netty.util.concurrent.DefaultPromise.notifyListeners(DefaultPromise.java:415)  
at io.netty.util.concurrent.DefaultPromise.setValue0(DefaultPromise.java:540)  
at io.netty.util.concurrent.DefaultPromise.setFailure0(DefaultPromise.java:533)  
at io.netty.util.concurrent.DefaultPromise.tryFailure(DefaultPromise.java:114)  
at io.netty.channel.nio.AbstractNioChannel$AbstractNioUnsafe$1.run(AbstractNioChannel.java:269)  
at io.netty.util.concurrent.PromiseTask$RunnableAdapter.call(PromiseTask.java:38)  
at io.netty.util.concurrent.ScheduledFutureTask.run(ScheduledFutureTask.java:127)  
at io.netty.util.concurrent.AbstractEventExecutor.safeExecute(AbstractEventExecutor.java:163)  
at io.netty.util.concurrent.SingleThreadEventExecutor.runAllTasks(SingleThreadEventExecutor.java:404)  
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:495)  
at io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:905)  
at java.base/java.lang.Thread.run(Unknown Source)  
Caused by: io.netty.channel.ConnectTimeoutException: connection timed out: /192.168.1.2:4840  
at io.netty.channel.nio.AbstractNioChannel$AbstractNioUnsafe$1.run(AbstractNioChannel.java:267)  
… 7 more

8.0.0 (b2019040718)  
Azul Systems, Inc. 11.0.2

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 8, 2019, 1:47am UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730/4 "2019-05-08T01:47:42Z")

</div>

This is just a standard network-level error. Ignition is trying to open a TCP connection and getting no response.

Make sure the server is running, you’ve got the right IP address, and there’s no firewall blocking any outbound connections. There’s nothing wrong with your configuration in Ignition right now.

---

<div class="post-metadata">

**Author:** ![shemelis.2013](https://avatars.discourse-cdn.com/v4/letter/s/5daacb/32.png) [@shemelis.2013](https://forum.inductiveautomation.com/u/shemelis.2013)\
**Post date:** [December 5, 2019, 4:53pm UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730/5 "2019-12-05T16:53:03Z")

</div>

How I am sure the OPC UA server is running properly or not?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [December 5, 2019, 4:54pm UTC](https://forum.inductiveautomation.com/t/opc-server-connection-status-faulted/24730/6 "2019-12-05T16:54:33Z")

</div>

Which OPC UA server? You should probably start a new topic with a more detailed question.