Update: Disabling ‘Certificate Validation Enabled’ fixed the problem for now. I guess the validation changed somewhere between 8.0.10 and 8.1.

I just upgraded Ignition to 8.1.0 and the connection to a OPC-UA server (TANI) stopped working.

The status page shows a certificate error. Thats strange, because security is set to None.

```auto
UaException: status=Bad_CertificateUriInvalid, message=The URI specified in the ApplicationDescription does not match the URI in the Certificate.
	at org.eclipse.milo.opcua.stack.core.util.validation.CertificateValidationUtil.checkApplicationUri(CertificateValidationUtil.java:685)
	at org.eclipse.milo.opcua.stack.client.security.DefaultClientCertificateValidator.validateCertificateChain(DefaultClientCertificateValidator.java:100)
	at org.eclipse.milo.opcua.sdk.client.api.identity.UsernameProvider.getIdentityToken(UsernameProvider.java:162)
	at org.eclipse.milo.opcua.sdk.client.session.SessionFsmFactory.activateSession(SessionFsmFactory.java:881)
	at org.eclipse.milo.opcua.sdk.client.session.SessionFsmFactory.lambda$configureActivatingState$17(SessionFsmFactory.java:345)
	at com.digitalpetri.strictmachine.dsl.ActionBuilder$PredicatedTransitionAction.execute(ActionBuilder.java:76)
	at com.digitalpetri.strictmachine.StrictMachine$PollAndEvaluate.lambda$run$0(StrictMachine.java:242)
	at java.base/java.util.ArrayList.forEach(Unknown Source)
	at com.digitalpetri.strictmachine.StrictMachine$PollAndEvaluate.run(StrictMachine.java:227)
	at java.base/java.util.concurrent.ThreadPoolExecutor.runWorker(Unknown Source)
	at java.base/java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)
	at java.base/java.lang.Thread.run(Unknown Source)

8.1.0 (b2020110211)
Azul Systems, Inc. 11.0.7

```

This message appears in the gateway log every few seconds

```auto
INFO | jvm 1 | 2020/11/29 16:53:30 | W [o.e.m.o.s.c.s.OpcUaBinaryStreamEncoder] [15:53:30]: Not a built-in type: class java.math.BigInteger 

```

Any ideas?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 29, 2020, 9:01pm UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/2 "2020-11-29T21:01:07Z")

</div>

It could be a legit mismatch between what’s in the certificate or what’s in the endpoints or it could be something else - can you get a Wireshark capture of the connection being made?

I’m not sure where the BigInteger thing is coming from… something in Ignition is sticking a BigInteger into an OPC write probably, but not sure offhand how to track that down.

---

<div class="post-metadata">

**Author:** ![chi](https://avatars.discourse-cdn.com/v4/letter/c/0ea827/32.png) [@chi](https://forum.inductiveautomation.com/u/chi)\
**Post date:** [November 30, 2020, 10:44am UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/3 "2020-11-30T10:44:56Z")

</div>

Here is the wireshark capture. On my test system i have a working connection to this UA-server, but i am not able to create a new one that is not faulted. Only visible difference is upper-lower case in the endpoint address (‘srv’ vs ‘SRV’).  
[opcua.zip](https://forum.inductiveautomation.com/uploads/short-url/mzZjZgsv4bY5XtXT4dUJUYjbXPE.zip) (3.4 KB)

Is there a logger that would help me trace the origin of thet BigInteger message?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 30, 2020, 11:14am UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/4 "2020-11-30T11:14:55Z")

</div>

> [@Kevin.Herron](#):
>
> something in Ignition is sticking a BigInteger into an OPC write probably

Jython doesn't use java.lang.Long by default for anything. Its `long()` type is implemented with BigInteger, so anything 64-bit passed to an untyped interface will be BigInteger.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 30, 2020, 11:37am UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/5 "2020-11-30T11:37:30Z")

</div>

TANI server is not configured correctly:

 ![wireshark](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/2/b2caa6f58d0200a921b9a4cdc9d6d245069e3a45.png)  
 ![cert](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/3/c343ecbffbb1c8a30dc13ef4322aa6df66e05776.jpeg)

The URI in the certificate must match the one in the ApplicationDescription returned in the endpoints. You said you are not using security, but you must be using a username and password, which in this case requires the server’s certificate be used to encrypt the credentials for transit and therefore requires that it is trusted and pass all validation checks.

---

<div class="post-metadata">

**Author:** ![chi](https://avatars.discourse-cdn.com/v4/letter/c/0ea827/32.png) [@chi](https://forum.inductiveautomation.com/u/chi)\
**Post date:** [November 30, 2020, 11:56am UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/6 "2020-11-30T11:56:33Z")

</div>

Thank you for your help.

The hostname of the virtual machine was changed since the first setup of the TANI server. I had to delete the certificate and restart the service to create a new certificate with the correct uri.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 30, 2020, 3:12pm UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/7 "2020-11-30T15:12:26Z")

</div>

> [@chi](#):
>
> The hostname of the virtual machine was changed since the first setup of the TANI server.

This is one reason Ignition no longer uses hostname or IP in the application URI it generates.

---

<div class="post-metadata">

**Author:** ![michel\_feria](https://avatars.discourse-cdn.com/v4/letter/m/ad7895/32.png) [@michel\_feria](https://forum.inductiveautomation.com/u/michel_feria)\
**Post date:** [March 21, 2023, 10:42am UTC](https://forum.inductiveautomation.com/t/opc-ua-connection-failed-after-upgrade-to-8-1-0-bad-certificateuriinvalid/41030/8 "2023-03-21T10:42:13Z")

</div>

Hi Kevin,

could you please give me more details how to configure TANI server?  
thanking you in advance

kind regards,