I am having issues following the set procedures for connecting a controlnet logix to a plc5. Here is the layout I have in both plc’s and in the opc-ua setup. What am I missing?  
Control Logix Setup  
0 - Processor  
1 - CNB/B  
—1 - CNB/B\_01\_CNET  
—2 - 1785 PLC5  
—3 - Drive  
—4 - 1785 PLC5  
2 - 1756 ENBT  
—IP xx.xx.xx.103

```
                 PLC 5 Setup

```

PLC5/80C  
PLC ControlNet Node - 2

DeviceName - Trimmer  
Timeout - 30000  
Timeout - 30000  
Timeout - 30000  
Enable Device - checked

HostName - xx.xx.xx.103  
Com Timeout - 10000  
Cache Timeout - 2400  
Connection Path - 1,1,2,1

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 25, 2011, 1:23am UTC](https://forum.inductiveautomation.com/t/opc-ua-controlnet-plc5/2544/2 "2011-01-25T01:23:21Z")

</div>

This isn’t currently supported but will be soon.

---

<div class="post-metadata">

**Author:** ![Jon.Trusik](https://avatars.discourse-cdn.com/v4/letter/j/d78d45/32.png) [@Jon.Trusik](https://forum.inductiveautomation.com/u/Jon.Trusik)\
**Post date:** [March 2, 2011, 1:31pm UTC](https://forum.inductiveautomation.com/t/opc-ua-controlnet-plc5/2544/3 "2011-03-02T13:31:14Z")

</div>

Any update on status of this feature?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 2, 2011, 3:38pm UTC](https://forum.inductiveautomation.com/t/opc-ua-controlnet-plc5/2544/4 "2011-03-02T15:38:34Z")

</div>

Should be available in 7.2.4 🙂

---

<div class="post-metadata">

**Author:** ![Jon.Trusik](https://avatars.discourse-cdn.com/v4/letter/j/d78d45/32.png) [@Jon.Trusik](https://forum.inductiveautomation.com/u/Jon.Trusik)\
**Post date:** [March 15, 2011, 6:50pm UTC](https://forum.inductiveautomation.com/t/opc-ua-controlnet-plc5/2544/5 "2011-03-15T18:50:58Z")

</div>

Is this working now in 7.2.4?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 15, 2011, 7:20pm UTC](https://forum.inductiveautomation.com/t/opc-ua-controlnet-plc5/2544/6 "2011-03-15T19:20:56Z")

</div>

You tell me! 😆

I saw Tom testing it, so it should be.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [March 16, 2011, 8:09pm UTC](https://forum.inductiveautomation.com/t/opc-ua-controlnet-plc5/2544/7 "2011-03-16T20:09:58Z")

</div>

Starting with version 7.2.4, connecting to PLC-5 and SLC processors through ControlNet and DH+ are both supported.

In your example above, your connection paths should be:  
1,1,2,2 to connect to PLC5 at ControlNet node 2  
1,1,2,4 to connect to PLC5 at ControlNet node 4

Connecting to ControlLogix, CompactLogix, PLC-5, SLC and MicroLogix processors using an IP address in the connection path is coming soon.