# OPC-UA endpoint change

**URL:** <https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457>\
**Category:** Ignition\
**Tags:** perspective, ignition81\
**Created:** [May 9, 2023, 8:24am UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457 "2023-05-09T08:24:32Z")\
**Posts on this page:** 15\
**Page:** 1

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 8:24am UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/1 "2023-05-09T08:24:32Z")

</div>

hi, I want to access the OPC-UA endpoint of Server 2 where the DB is installed from Server 1.

But access is denied.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/8/582656512452ff5eba7b3552461cd5a4760d9659.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/b/5b7e3d1cc79fa9a368b7a334671362d8e4b5da44.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/9/d91a6fc81dfc16ab527ba78038c11d6e3db71b94.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/7/a736c49b44ffafd379452697637823ac1e1ffa6d.png)

Portforwarding is complete.

Thanks for reading.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 9, 2023, 1:24pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/2 "2023-05-09T13:24:52Z")

</div>

After changing these settings on the server a restart is necessary.

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 2:01pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/3 "2023-05-09T14:01:36Z")

</div>

sure. I have already done it

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 2:04pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/4 "2023-05-09T14:04:17Z")

</div>

Is there anything else to check?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 9, 2023, 3:15pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/5 "2023-05-09T15:15:54Z")

</div>

Firewall on both servers maybe?

Right now you have a networking error that means either the server isn't listening on the address/port specified or that a firewall is blocking the connection or something.

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 3:42pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/6 "2023-05-09T15:42:05Z")

</div>

um..

> [@Kevin.Herron](#):
>
> Right now you have a networking error that means either the server isn't listening on the address/port specified or that a firewall is blocking the connection or something.

The IP address in the picture above was tested with my server IP address. localhost works, but I can't directly enter my IP address. Is this also a firewall issue?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 9, 2023, 3:42pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/7 "2023-05-09T15:42:57Z")

</div>

Maybe, but usually that means you didn't restart the Ignition Gateway after changing the settings.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 9, 2023, 3:44pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/8 "2023-05-09T15:44:07Z")

</div>

To be clear - you are changing the server settings (first screenshot) on Server 2, have restarted Server 2, and now you're on Server 1 trying to make an OPC UA client connection _to_ Server 2?

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 3:44pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/9 "2023-05-09T15:44:35Z")

</div>

> [@Kevin.Herron](#):
>
> you didn't restart the Ignition Gateway

Is gateway restart the way to restart ignition from window service? If this is the right way, I did.

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 3:45pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/10 "2023-05-09T15:45:43Z")

</div>

> [@Kevin.Herron](#):
>
> you are changing the server settings (first screenshot) on Server 2, have restarted Server 2, and now you're on Server 1 trying to make an OPC UA client connection _to_ Server 2

If the above method is correct, yes. I did it

---

<div class="post-metadata">

**Author:** ![avaughn](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/avaughn/32/38972_2.png) [@avaughn](https://forum.inductiveautomation.com/u/avaughn)\
**Post date:** [May 9, 2023, 3:47pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/11 "2023-05-09T15:47:55Z")

</div>

Instead of using a list of addresses for the bind address, what if you just use the 192.168.0.7 IP or 0.0.0.0? You would have to restart again after making that change.

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 3:51pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/12 "2023-05-09T15:51:49Z")

</div>

> [@avaughn](#):
>
> what if you just use the 192.168.0.7 IP or 0.0.0.0?

ok. but I can't try it because it's not my office right now (I'm in Korea). I'll try it after I get back.

Thank you for answer!

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 3:53pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/13 "2023-05-09T15:53:11Z")

</div>

I can't try it because it's not my office right now (I'm in Korea). After coming back, I'll try reviewing the firewall and restarting the gateway again. Thank you for answer!

---

<div class="post-metadata">

**Author:** ![avaughn](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/avaughn/32/38972_2.png) [@avaughn](https://forum.inductiveautomation.com/u/avaughn)\
**Post date:** [May 9, 2023, 3:53pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/14 "2023-05-09T15:53:14Z")

</div>

I think I actually am incorrect about not being able to pass a list to that configuration, but I was thinking maybe only the first address is successfully binding. Do you have the full logfile available that you could share?

---

<div class="post-metadata">

**Author:** ![KIM\_SUNG\_HOO](https://avatars.discourse-cdn.com/v4/letter/k/977dab/32.png) [@KIM\_SUNG\_HOO](https://forum.inductiveautomation.com/u/KIM_SUNG_HOO)\
**Post date:** [May 9, 2023, 3:55pm UTC](https://forum.inductiveautomation.com/t/opc-ua-endpoint-change/73457/15 "2023-05-09T15:55:03Z")

</div>

> [@avaughn](#):
>
> Do you have the full logfile available that you could share?

it's not my office right now.

I'm not in the office right now so I can't show you the log file. If it doesn't work after trying the above, I'll contact you with the log file.