Hi Dear Ignition team

I have 2 PC with kepware opc servers and one PC with Ignition ,

In Ignition settings opc servers part i added one opc-ua as main server and second as failover but when

the main opc server is fails the Ignition is not connection to failover opc

connection with both opc servers is ok i try to add both as separate opc servers in Ignition  
can you help me setup this option.

Thanks in advance

---

<div class="post-metadata">

**Author:** ![zackscriven](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zackscriven/32/7213_2.png) [@zackscriven](https://forum.inductiveautomation.com/u/zackscriven)\
**Post date:** [March 23, 2014, 7:07pm UTC](https://forum.inductiveautomation.com/t/opc-ua-failover-problem/8083/2 "2014-03-23T19:07:40Z")

</div>

Is the connection of the first OPC server going to “failed”

Is the same project file loaded on both kepware servers?  
Are they using the same password?

---

<div class="post-metadata">

**Author:** ![anna](https://avatars.discourse-cdn.com/v4/letter/a/779978/32.png) [@anna](https://forum.inductiveautomation.com/u/anna)\
**Post date:** [June 2, 2014, 9:47pm UTC](https://forum.inductiveautomation.com/t/opc-ua-failover-problem/8083/3 "2014-06-02T21:47:30Z")

</div>

Also, do both have Ignition’s certificate as “Trusted”?

Additionally, a log export would help.