I am getting following error.

Returning ServiceFault for request: com.inductiveautomation.opcua.types.messages.ActivateSessionRequest@5c3d1b49. StatusCode=StatusCode[Severity=Bad, Subcode=Bad\_UserAccessDenied]

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [January 5, 2020, 11:57pm UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/2 "2020-01-05T23:57:30Z")

</div>

Welcome to the forum…

please supply more detail such as Ignition version, new install or existing install has suddenly stopped…

---

<div class="post-metadata">

**Author:** ![pratikme1](https://avatars.discourse-cdn.com/v4/letter/p/ee59a6/32.png) [@pratikme1](https://forum.inductiveautomation.com/u/pratikme1)\
**Post date:** [January 6, 2020, 12:18am UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/3 "2020-01-06T00:18:02Z")

</div>

It is existing install. Ignition version **7.9.8**. It suddenly stopped working today. I restarted the OPC UA module. But no success in it.

 ![Capture](https://us1.discourse-cdn.com/inductiveautomation/original/2X/4/4fb01cbd1e3707b7067fa47b8863401c01b08f7e.png)

Thanks and looking forward to your help

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 6, 2020, 1:15am UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/4 "2020-01-06T01:15:02Z")

</div>

This error suggests your connection is configured with the wrong username and password for the server it’s connecting to.

If it’s the local Ignition server then make sure it’s either the default of opcuauser/password or check to see if someone has changed the authentication profile used by the server.

---

<div class="post-metadata">

**Author:** ![kairongsen](https://avatars.discourse-cdn.com/v4/letter/k/eb9ed0/32.png) [@kairongsen](https://forum.inductiveautomation.com/u/kairongsen)\
**Post date:** [January 6, 2020, 8:03am UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/5 "2020-01-06T08:03:50Z")

</div>

May I know what type of OS you are running Ignition on it?  
If you installed your Ignition inside your window 10, probably will encounter this issue. Months ago I have the same issue for Window 10. My solution is I migrate my Ignition into window server 2012 R2 and everything is fine now.

---

<div class="post-metadata">

**Author:** ![pratikme1](https://avatars.discourse-cdn.com/v4/letter/p/ee59a6/32.png) [@pratikme1](https://forum.inductiveautomation.com/u/pratikme1)\
**Post date:** [January 6, 2020, 1:42pm UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/6 "2020-01-06T13:42:38Z")

</div>

It’s on windows server 2016.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/9/9570648243b95b3a7f08f81763bfe443ab21791d.jpeg)

---

<div class="post-metadata">

**Author:** ![kairongsen](https://avatars.discourse-cdn.com/v4/letter/k/eb9ed0/32.png) [@kairongsen](https://forum.inductiveautomation.com/u/kairongsen)\
**Post date:** [January 7, 2020, 2:14am UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/7 "2020-01-07T02:14:21Z")

</div>

Possible that the OS went through some update and change its network security setting?

---

<div class="post-metadata">

**Author:** ![keith.crenshaw](https://avatars.discourse-cdn.com/v4/letter/k/fbc32d/32.png) [@keith.crenshaw](https://forum.inductiveautomation.com/u/keith.crenshaw)\
**Post date:** [September 23, 2020, 11:51pm UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/8 "2020-09-23T23:51:32Z")

</div>

Having this same issue on a 7.9.14 gateway, which I updated to 7.9.16. I have tried to remapping the Endpoint to the ones that are discovered on localhost as well as setting the default password again.

UaServiceFaultException: status=Bad\_UserAccessDenied, message=User does not have permission to perform the requested operation. at org.eclipse.milo.opcua.stack.client.UaStackClient.lambda$deliverResponse$5(UaStackClient.java:273) at org.eclipse.milo.opcua.stack.core.util.ExecutionQueue$Task.run(ExecutionQueue.java:119) at java.util.concurrent.ThreadPoolExecutor.runWorker(Unknown Source) at java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source) at java.lang.Thread.run(Unknown Source)

---

<div class="post-metadata">

**Author:** ![kilroywashere](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kilroywashere/32/28674_2.png) [@kilroywashere](https://forum.inductiveautomation.com/u/kilroywashere)\
**Post date:** [October 29, 2021, 9:23pm UTC](https://forum.inductiveautomation.com/t/opc-ua-server-connection-faulted/31070/9 "2021-10-29T21:23:54Z")

</div>

Hello - I just encountered the same issue on an existing install. Wondering if you ever found a solution?