Hi Guys,

I’m trying to connect to a old PLC5/250 through ControlNet and DH+. But I’m not sure if my connection path is correct and whether our arrangement is even supported by ignition. Could someone have a look at this for me please?

Below is the path to PLC 5 and my connection path is 1,10,2,5,1,4,3,1  
 ![PLC5 Connection Path](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/7/77c41bea69a3125e2e7e01f211aa5e83f70da7e1.png)

---

<div class="post-metadata">

**Author:** ![schenk](https://avatars.discourse-cdn.com/v4/letter/s/6bbea6/32.png) [@schenk](https://forum.inductiveautomation.com/u/schenk)\
**Post date:** [October 8, 2020, 8:55pm UTC](https://forum.inductiveautomation.com/t/opc-ua-to-plc5-250-controlnet-dh/39515/2 "2020-10-08T20:55:21Z")

</div>

I believe you just need to add a 0 to the end of the path to reach the processor

---

<div class="post-metadata">

**Author:** ![Morgan](https://avatars.discourse-cdn.com/v4/letter/m/0ea827/32.png) [@Morgan](https://forum.inductiveautomation.com/u/Morgan)\
**Post date:** [October 8, 2020, 9:00pm UTC](https://forum.inductiveautomation.com/t/opc-ua-to-plc5-250-controlnet-dh/39515/3 "2020-10-08T21:00:30Z")

</div>

thanks, i just tried it but no luck. anyways, i’ve got it working through RSLinx OPC topic now.