# Passing Minor Alarm data to Ignition

**URL:** <https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721>\
**Category:** Ignition\
**Created:** [September 2, 2022, 5:00pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721 "2022-09-02T17:00:49Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![kaleb.s](https://avatars.discourse-cdn.com/v4/letter/k/f08c70/32.png) [@kaleb.s](https://forum.inductiveautomation.com/u/kaleb.s)\
**Post date:** [September 2, 2022, 5:00pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/1 "2022-09-02T17:00:49Z")

</div>

Is there a specific process to pass minor fault codes from a PLC to a Ignition Dashboard? Is it as simple as having a Minor Fault tag in the PLC logic and coding a tag in ignition to connect to the PLC tag and display the minor fault data via a label of sorts on ignition?

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 2, 2022, 5:17pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/2 "2022-09-02T17:17:22Z")

</div>

Might want to give details on your specific PLC(s)

---

<div class="post-metadata">

**Author:** ![kaleb.s](https://avatars.discourse-cdn.com/v4/letter/k/f08c70/32.png) [@kaleb.s](https://forum.inductiveautomation.com/u/kaleb.s)\
**Post date:** [September 2, 2022, 5:27pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/3 "2022-09-02T17:27:27Z")

</div>

PLC is Allen Bradley L310ER

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 2, 2022, 5:29pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/4 "2022-09-02T17:29:36Z")

</div>

My vote is to use GSVs in your PLC and get the fault info into a tag or UDT and then just read these tags in Ignition. If you create a UDT in the PLC you can create a UDT in Ignition to match, which makes creating tags in Ignition simple and quick and easy to maintain.

---

<div class="post-metadata">

**Author:** ![kaleb.s](https://avatars.discourse-cdn.com/v4/letter/k/f08c70/32.png) [@kaleb.s](https://forum.inductiveautomation.com/u/kaleb.s)\
**Post date:** [September 2, 2022, 5:38pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/5 "2022-09-02T17:38:04Z")

</div>

Appreciate the help!

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 2, 2022, 5:41pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/6 "2022-09-02T17:41:45Z")

</div>

That is just my opinion, others may have some help as well

Welcome to the forum by the way.

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [September 2, 2022, 6:16pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/7 "2022-09-02T18:16:56Z")

</div>

Be sure to put it in the fault handling routine.

Also there’s a spreadsheet that may be of use to you.

[https://literature.rockwellautomation.com/idc/groups/literature/documents/rd/1756-rd001\_-en-p.xlsx](https://literature.rockwellautomation.com/idc/groups/literature/documents/rd/1756-rd001_-en-p.xlsx)

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 2, 2022, 6:29pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/8 "2022-09-02T18:29:29Z")

</div>

If you are only wanting minor fault info there isn’t a need for using a fault handler routine. Wanting major faults would though.

---

<div class="post-metadata">

**Author:** ![kaleb.s](https://avatars.discourse-cdn.com/v4/letter/k/f08c70/32.png) [@kaleb.s](https://forum.inductiveautomation.com/u/kaleb.s)\
**Post date:** [September 2, 2022, 7:36pm UTC](https://forum.inductiveautomation.com/t/passing-minor-alarm-data-to-ignition/63721/9 "2022-09-02T19:36:23Z")

</div>

I downloaded that spreadsheet today actually haha. Thank you for the recommendation though!