I installed 8.3 and noticed Perspective is missing in the Project Browser. I tried uninstalling and reinstalling and it is still missing. This is purely for testing and not impacting anything, just wondering if anyone else has this issue.

 ![Screenshot 2025-08-06 065142](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/f/af27c8532bc06fb177cf9d2c105192427ee3eaea.png)

---

<div class="post-metadata">

**Author:** ![avaughn](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/avaughn/32/38972_2.png) [@avaughn](https://forum.inductiveautomation.com/u/avaughn)\
**Post date:** [August 6, 2025, 1:57pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/2 "2025-08-06T13:57:03Z")

</div>

Could you confirm that the Perspective module is showing as installed on the Gateway webpage?

If it is, then can you open the designer console and check for any errors?

Edit: You could also start with checking the designer console since you're already there.

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 2:43pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/3 "2025-08-06T14:43:36Z")

</div>

Yes, it is installed and in trial mode. I do see errors in the console.

 ![Screenshot 2025-08-06 074256](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/0/10775838edea18b81efd103f3a5331e80100d8b9.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 6, 2025, 2:44pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/4 "2025-08-06T14:44:50Z")

</div>

Can you attach the rest of that log output? The more meaningful log message is probably "Failed to start Browser Engine" and whatever comes after it.

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 3:00pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/5 "2025-08-06T15:00:18Z")

</div>

```python
07:41:57.230 [Designer-Startup] INFO designer.main -- Downloading... [+0]
07:41:57.293 [Designer-Startup] INFO designer.main -- Cleanup... [+64]
07:41:57.304 [Designer-Startup] INFO designer.main -- Initializing UI... [+75]
07:41:57.396 [DesignerExecEngine-1] INFO tags.subscriptions -- Changing connected quality to 'Good'
07:41:59.156 [Designer-Startup] INFO designer.main -- Starting module: Perspective [+1927]
07:42:01.066 [Designer-Startup] INFO Perspective.Designer -- Starting up Perspective module. Mode: Trial
07:42:01.823 [Designer-Startup] ERROR designer.JXBrowserUtil -- Failed to start Browser Engine with options
 com.teamdev.jxbrowser.engine.EngineOptions:
  autoplayEnabled: false
  chromiumDir: C:\Users\[REDACTED]\.ignition\cache\resources\jxbrowser\8.5.0
  chromiumSwitches: []
  diskCacheSize: <unknown>
  fileAccessFromFilesAllowed: false
  isGpuDisabled: false
  isIncognitoEnabled:true
  language:en-us
  passwordStore: <unknown>
  remoteDebugginPort: 9222
  renderingMode: OFF_SCREEN
  isSandboxDisabled: false
  secureOriginWhitelist: []
  isTouchMenuEnabled: false
  userAgent: <unknown user agent value>
  userDataDir:C:\Users\[REDACTED]\AppData\Local\Temp\JxBrowser-UserData-332325d3-c85e-456d-8321-86373d8326e5
  webSecurityDisabled: false
.
com.teamdev.jxbrowser.engine.ChromiumProcessStartupFailureException: Process exit code: -2147483645
	at com.teamdev.jxbrowser.engine.internal.EngineImpl.newInstance(EngineImpl.java:282)
	at com.teamdev.jxbrowser.engine.Engine.newInstance(Engine.java:163)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.lambda$getOrCreateEngine$2(JxBrowserUtil.java:352)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.runResourceLockedAction(JxBrowserUtil.java:558)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.getOrCreateEngine(JxBrowserUtil.java:352)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.getOrCreateEngine(JxBrowserUtil.java:417)
	at com.inductiveautomation.perspective.designer.DesignerHook.startup(DesignerHook.java:233)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner$LoadedModule.startup(IgnitionDesigner.java:2006)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner.startupModule(IgnitionDesigner.java:1202)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner.loadProject(IgnitionDesigner.java:1005)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner$StartupProjectDialogHandler.lambda$new$2(IgnitionDesigner.java:2050)
	at java.base/java.lang.Thread.run(Unknown Source)
07:42:01.825 [Designer-Startup] INFO designer.main -- Starting module: Vision [+4596]
07:42:02.682 [Designer-Startup] ERROR designer.JXBrowserUtil -- Failed to start Browser Engine with options
 com.teamdev.jxbrowser.engine.EngineOptions:
  autoplayEnabled: false
  chromiumDir: C:\Users\[REDACTED]\.ignition\cache\resources\jxbrowser\8.5.0
  chromiumSwitches: []
  diskCacheSize: <unknown>
  fileAccessFromFilesAllowed: false
  isGpuDisabled: false
  isIncognitoEnabled:true
  language:en-us
  passwordStore: <unknown>
  remoteDebugginPort: 9222
  renderingMode: OFF_SCREEN
  isSandboxDisabled: false
  secureOriginWhitelist: []
  isTouchMenuEnabled: false
  userAgent: <unknown user agent value>
  userDataDir:C:\Users\[REDACTED]\AppData\Local\Temp\JxBrowser-UserData-8899eb31-8351-46da-9e3f-9de9cf1fd468
  webSecurityDisabled: false
.
com.teamdev.jxbrowser.engine.ChromiumProcessStartupFailureException: Process exit code: -2147483645
	at com.teamdev.jxbrowser.engine.internal.EngineImpl.newInstance(EngineImpl.java:282)
	at com.teamdev.jxbrowser.engine.Engine.newInstance(Engine.java:163)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.lambda$getOrCreateEngine$2(JxBrowserUtil.java:352)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.runResourceLockedAction(JxBrowserUtil.java:558)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.getOrCreateEngine(JxBrowserUtil.java:352)
	at com.inductiveautomation.ignition.client.util.JxBrowserUtil.getOrCreateEngine(JxBrowserUtil.java:417)
	at com.inductiveautomation.webbrowser.BrowserInstanceManager.startup(BrowserInstanceManager.java:36)
	at com.inductiveautomation.factorypmi.application.FPMIApp.createApp(FPMIApp.java:336)
	at com.inductiveautomation.factorypmi.designer.model.VisionDesignerImpl.createRoot(VisionDesignerImpl.java:704)
	at com.inductiveautomation.factorypmi.designer.model.VisionDesignerImpl.startup(VisionDesignerImpl.java:364)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner$LoadedModule.startup(IgnitionDesigner.java:2006)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner.startupModule(IgnitionDesigner.java:1202)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner.loadProject(IgnitionDesigner.java:1005)
	at com.inductiveautomation.ignition.designer.IgnitionDesigner$StartupProjectDialogHandler.lambda$new$2(IgnitionDesigner.java:2050)
	at java.base/java.lang.Thread.run(Unknown Source)
07:42:02.682 [Designer-Startup] ERROR WebBrowser -- BrowserEngine was not initialized. Web Browser Component can not start!

```

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 6, 2025, 3:02pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/6 "2025-08-06T15:02:26Z")

</div>

What version of Windows are you using? Any AV software or Windows Defender running?

If it's not an unsupported OS then AV software preventing the Chromium process from being started is often the cause.

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 3:06pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/7 "2025-08-06T15:06:16Z")

</div>

Windows 11. I had a later version of 8.1 installed with no issues, this PC is where I do the bulk of my development.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 6, 2025, 3:07pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/8 "2025-08-06T15:07:41Z")

</div>

You can try deleting the cache dir in that path and launching again.

JXBrowser / Chromium was upgraded in 8.3, so it's a new executable/signature that may be an issue for the AV software.

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 3:15pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/9 "2025-08-06T15:15:00Z")

</div>

I deleted it and I still get the same error.

---

<div class="post-metadata">

**Author:** ![jcoffman](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jcoffman/32/6429_2.png) [@jcoffman](https://forum.inductiveautomation.com/u/jcoffman)\
**Post date:** [August 6, 2025, 3:21pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/10 "2025-08-06T15:21:12Z")

</div>

I also suspect that something on your machine is preventing the chromium process from running, probably AV.

you can try adding `-Dignition.client.jxBrowser.logLevel=DEBUG` to the [JVM Arguments in the Designer Launcher](https://docs.inductiveautomation.com/docs/8.1/launchers-and-workstation/designer-launcher#designer-general-settings) which should result in more output, however i don't know how much in this scenario as we are dependent on JxBrowser logging for this.

I would definitely look into your AV or security policies related to chromium though

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 3:42pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/11 "2025-08-06T15:42:54Z")

</div>

Ok, I will reach out to our IT and report back 🙂

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 9:04pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/12 "2025-08-06T21:04:54Z")

</div>

Ok, we “snoozed” our AV software and it still did not correct the issue.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [August 6, 2025, 9:15pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/13 "2025-08-06T21:15:49Z")

</div>

> [@EMarsupial](#):
>
> I deleted it and I still get the same error.

Which directory did you remove, specifically?  
Try removing both:

```python
C:\Users\[REDACTED]\AppData\Local\Temp\JxBrowser-UserData-332325d3-c85e-456d-8321-86373d8326e5
C:\Users\[REDACTED]\.ignition\cache\resources\jxbrowser\

```

And any other jxbrowser directories you see in `C:\Users\[REDACTED]\AppData\Local\Temp\`

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [August 6, 2025, 9:26pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/14 "2025-08-06T21:26:19Z")

</div>

> [@paul-griffith](#):
>
> `C:\Users\[REDACTED]\.ignition\cache\resources\jxbrowser\`

I deleted:

C:\Users\[REDACTED]\.ignition\cache\resources\jxbrowser\

I don’t have:

C:\Users\[REDACTED]\AppData\Local\Temp\JxBrowser-UserData-332325d3-c85e-456d-8321-86373d8326e5

I installed Ignition in a separate windows 10 VM without any issues.

---

<div class="post-metadata">

**Author:** ![bas.bekker](https://avatars.discourse-cdn.com/v4/letter/b/13edae/32.png) [@bas.bekker](https://forum.inductiveautomation.com/u/bas.bekker)\
**Post date:** [October 31, 2025, 1:36pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/15 "2025-10-31T13:36:00Z")

</div>

I had the issue as well and I downloaded the designer using the new gateway (multiple times). After looking for a few hours I tried downloading the designer from the inductive website and guess what. there was perspective again. So I don’t know why but it appears installing the designer/upgrading the designer works better straight from the inductive website.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [October 31, 2025, 4:03pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/16 "2025-10-31T16:03:49Z")

</div>

The Designer _Launcher_ you download from a given gateway doesn't actually hold anything related to the actual Designer application. Every time you launch the Designer _via_ the Designer Launcher, you're launching a separate application that is attached/coupled to the specific gateway you're connecting to.

Whatever happened to make your system work was not related to upgrading/installing a new designer launcher, guaranteed.

---

<div class="post-metadata">

**Author:** ![bas.bekker](https://avatars.discourse-cdn.com/v4/letter/b/13edae/32.png) [@bas.bekker](https://forum.inductiveautomation.com/u/bas.bekker)\
**Post date:** [November 3, 2025, 7:34am UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/17 "2025-11-03T07:34:40Z")

</div>

Thank you for your reply paul-griffith. I had the same issue on two systems with the same solution to both systems. So sommething must have gotten across with the install from the inductive website. I can’t tell you what happened only what I did and that it fixed the issue.

---

<div class="post-metadata">

**Author:** ![Oscar\_Palazon](https://avatars.discourse-cdn.com/v4/letter/o/5daacb/32.png) [@Oscar\_Palazon](https://forum.inductiveautomation.com/u/Oscar_Palazon)\
**Post date:** [November 16, 2025, 7:49am UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/18 "2025-11-16T07:49:07Z")

</div>

I had the same problem, but now it seems it has been resolved, although I'm not sure if it was thanks to something I did.

When I opened Designer for the first time after installing it (Windows 11) from the gateway wizard, it opened directly without loading any projects.

At that point, I saw that the Perspective module did not appear in the project tree, even though it was installed.

After closing Designer and reopening it with the “samplequickstart” project, the Perspective module appeared in the tree.

I then created a new empty project with all the default paths, and the Perspective module still appeared, so it seems that this solves the problem.

I hope this helps you resolve the issue.

---

<div class="post-metadata">

**Author:** ![cjbrading](https://avatars.discourse-cdn.com/v4/letter/c/da6949/32.png) [@cjbrading](https://forum.inductiveautomation.com/u/cjbrading)\
**Post date:** [December 14, 2025, 9:07am UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/19 "2025-12-14T09:07:42Z")

</div>

I had the same issue with version 8.3.2 on W11 - downloading the Designer Launcher from the IA site also fixed it for me.

---

<div class="post-metadata">

**Author:** ![EMarsupial](https://avatars.discourse-cdn.com/v4/letter/e/f07891/32.png) [@EMarsupial](https://forum.inductiveautomation.com/u/EMarsupial)\
**Post date:** [December 15, 2025, 3:04pm UTC](https://forum.inductiveautomation.com/t/perspective-missing-in-project-browser/109429/21 "2025-12-15T15:04:30Z")

</div>

@cjbrading I tried the same thing and it did not work for me.