# Phantom Alarms showing in Alarm Status Table

**URL:** <https://forum.inductiveautomation.com/t/phantom-alarms-showing-in-alarm-status-table/37346>\
**Category:** Ignition\
**Tags:** ignition79\
**Created:** [August 4, 2020, 7:13am UTC](https://forum.inductiveautomation.com/t/phantom-alarms-showing-in-alarm-status-table/37346 "2020-08-04T07:13:25Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![nminchin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nminchin/32/6911_2.png) [@nminchin](https://forum.inductiveautomation.com/u/nminchin)\
**Post date:** [August 4, 2020, 7:13am UTC](https://forum.inductiveautomation.com/t/phantom-alarms-showing-in-alarm-status-table/37346/1 "2020-08-04T07:13:25Z")

</div>

v7.9.14

I’m seeing some phantom alarms at a customer’s site.  
I have an analogue transmitter with a high digital tag with single alarm attached which is on, but I also have a second copy showing in the alarm status table of the exact same alarm. However, I’m not able to get rid of it and acknowledgment fails for it. This is affecting a range of other tags as well, not just this one analogue.  
If I turn off the high tag, the first alarm goes away, but the second remains there. The alarm sources are identical…  
I’ve tried restarting the tag provider and the OPC-UA server with no effect. I haven’t yet rebooted the gateway as I’ll need to let the site know. Is there something else I can do short of reboot gateway?  
What module drives these alarms?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/9/b963af0d946de3fb7f9bb0f70fe6e0c2c819cb84.png)

---

<div class="post-metadata">

**Author:** ![Mau89](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mau89/32/20680_2.png) [@Mau89](https://forum.inductiveautomation.com/u/Mau89)\
**Post date:** [September 28, 2022, 4:25pm UTC](https://forum.inductiveautomation.com/t/phantom-alarms-showing-in-alarm-status-table/37346/2 "2022-09-28T16:25:13Z")

</div>

Same problem on 8.1.17

---

<div class="post-metadata">

**Author:** ![scott.ashby](https://avatars.discourse-cdn.com/v4/letter/s/b9e5f3/32.png) [@scott.ashby](https://forum.inductiveautomation.com/u/scott.ashby)\
**Post date:** [October 11, 2022, 7:32pm UTC](https://forum.inductiveautomation.com/t/phantom-alarms-showing-in-alarm-status-table/37346/3 "2022-10-11T19:32:41Z")

</div>

We need to get a fix to this. Almost ever single project I have ever developed has had this issue and I can't remember how tech support fixed if for me.

---

<div class="post-metadata">

**Author:** ![wildbilly](https://avatars.discourse-cdn.com/v4/letter/w/e19adc/32.png) [@wildbilly](https://forum.inductiveautomation.com/u/wildbilly)\
**Post date:** [November 18, 2022, 4:14am UTC](https://forum.inductiveautomation.com/t/phantom-alarms-showing-in-alarm-status-table/37346/4 "2022-11-18T04:14:30Z")

</div>

right click restart tag from designer tag browser usually clears them for me