Hi, i have connected my PLC(Rockwell) in ignition using Allen-Bradley Logix Driver and its working fine. Anyone know what is the driver in Kepware server that equivalente to this?

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [July 8, 2024, 3:42pm UTC](https://forum.inductiveautomation.com/t/plc-allen-bradley-logix-driver/92900/2 "2024-07-08T15:42:21Z")

</div>

Allen Bradley ControlLogix Ethernet

Also, when you add the device make sure to just choose the model based on name, and ignore the numbers after becaues even though the 5500 is an old model, they still refer to it. Most likely you're not using an ENI module either, so don't select one of those.

---

<div class="post-metadata">

**Author:** ![TechEnlive](https://avatars.discourse-cdn.com/v4/letter/t/3be4f8/32.png) [@TechEnlive](https://forum.inductiveautomation.com/u/TechEnlive)\
**Post date:** [July 9, 2024, 7:50am UTC](https://forum.inductiveautomation.com/t/plc-allen-bradley-logix-driver/92900/3 "2024-07-09T07:50:16Z")

</div>

Thanks for reply but i am stuck here. I have been tried ControllLogix 5500 and CompactLogix 5300 but tag quality Bad.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/1/e151da70537e6eff8695fb5a36b37f2fd7af8b5c.png)

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [July 9, 2024, 9:39am UTC](https://forum.inductiveautomation.com/t/plc-allen-bradley-logix-driver/92900/4 "2024-07-09T09:39:26Z")

</div>

Without _showing_ us what you've tried, or even the PLC model, it's not easy to give advice.  
But, here's an example:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/2/d2018c0533751619d8b13398de63ef259173fdfc.png)

---

<div class="post-metadata">

**Author:** ![TechEnlive](https://avatars.discourse-cdn.com/v4/letter/t/3be4f8/32.png) [@TechEnlive](https://forum.inductiveautomation.com/u/TechEnlive)\
**Post date:** [July 9, 2024, 11:34am UTC](https://forum.inductiveautomation.com/t/plc-allen-bradley-logix-driver/92900/5 "2024-07-09T11:34:29Z")

</div>

The model of PLC 1756-L63 and i have tried with both Control Logix and Compact Logix.  
Thanks for your help. I got the soluciton and the issue was with Logix Options.