# PLC - Ignition Connection (Disconnected: Protocol: EIP - Run Mode)

**URL:** <https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [October 22, 2024, 3:40pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619 "2024-10-22T15:40:57Z")\
**Posts on this page:** 19\
**Page:** 1

<div class="post-metadata">

**Author:** ![pkhoshroo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pkhoshroo/32/26801_2.png) [@pkhoshroo](https://forum.inductiveautomation.com/u/pkhoshroo)\
**Post date:** [October 22, 2024, 3:40pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/1 "2024-10-22T15:40:57Z")

</div>

Hello everyone,

I am trying to connect my PLC to Ignition, but I get the error message below. My Ignition Designer is in a VM, and I can ping the PLC IP address from that VM. Does anyone have information on how to resolve this? Thank you!

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/4/a425cada11a8595218e850e3ad7cff0a04cdf823.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [October 22, 2024, 3:49pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/2 "2024-10-22T15:49:25Z")

</div>

The gateway makes the connection to the PLC, not the designer.

- Can you ping from the gateway to the PLC?

- What firmware is in the PLC? (If \>20, you are using the wrong driver.)

---

<div class="post-metadata">

**Author:** ![pkhoshroo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pkhoshroo/32/26801_2.png) [@pkhoshroo](https://forum.inductiveautomation.com/u/pkhoshroo)\
**Post date:** [October 22, 2024, 4:54pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/3 "2024-10-22T16:54:05Z")

</div>

> [@pturmel](#):
>
> What firmware is in the PLC?

You are correct I was using the wrong driver, thank you for your help!

---

<div class="post-metadata">

**Author:** ![balandeganesh123](https://avatars.discourse-cdn.com/v4/letter/b/7c8e57/32.png) [@balandeganesh123](https://forum.inductiveautomation.com/u/balandeganesh123)\
**Post date:** [May 2, 2026, 9:25am UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/4 "2026-05-02T09:25:47Z")

</div>

Hi,  
I am facing the same kind of issue.

**Connecting : Protocol: EIP - Run Mode.**

Could you please help me understand what this means and suggest a solution?

---

<div class="post-metadata">

**Author:** ![bobby.miller](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bobby.miller/32/85153_2.png) [@bobby.miller](https://forum.inductiveautomation.com/u/bobby.miller)\
**Post date:** [May 2, 2026, 11:48am UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/5 "2026-05-02T11:48:58Z")

</div>

This is a question about your logix version. What version of RSLogix and/or Studio are you using? Depending on this, you will want to change which driver version you apply. Rockwell changed their driver interface around the 20/21 version split.

---

<div class="post-metadata">

**Author:** ![balandeganesh123](https://avatars.discourse-cdn.com/v4/letter/b/7c8e57/32.png) [@balandeganesh123](https://forum.inductiveautomation.com/u/balandeganesh123)\
**Post date:** [May 2, 2026, 10:14pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/6 "2026-05-02T22:14:40Z")

</div>

I'm currently using studio 5000 V32.01

And my plc is 5380 compact logix (5069-L330ER)

---

<div class="post-metadata">

**Author:** ![bobby.miller](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bobby.miller/32/85153_2.png) [@bobby.miller](https://forum.inductiveautomation.com/u/bobby.miller)\
**Post date:** [May 2, 2026, 10:30pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/7 "2026-05-02T22:30:49Z")

</div>

Perfect. Make sure you are connecting using this driver:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/0/b0fb8735ef0f4a0e03666a1cf89aa925864f4b84.png)

---

<div class="post-metadata">

**Author:** ![balandeganesh123](https://avatars.discourse-cdn.com/v4/letter/b/7c8e57/32.png) [@balandeganesh123](https://forum.inductiveautomation.com/u/balandeganesh123)\
**Post date:** [May 2, 2026, 10:51pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/8 "2026-05-02T22:51:03Z")

</div>

Ok I'll check and let you know

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 12, 2026, 11:11am UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/9 "2026-05-12T11:11:18Z")

</div>

A post was split to a new topic: [Problem connecting to S7-1500](https://forum.inductiveautomation.com/t/problem-connecting-to-s7-1500/115487)

---

<div class="post-metadata">

**Author:** ![Enrique\_Torres](https://avatars.discourse-cdn.com/v4/letter/e/ad7895/32.png) [@Enrique\_Torres](https://forum.inductiveautomation.com/u/Enrique_Torres)\
**Post date:** [September 15, 2026, 3:16pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/10 "2026-09-15T15:16:03Z")

</div>

good morning...i have somwhat of a similar issue...i keep losing communication to my PLC. Everything goes red for a few seconds and in the Gateway i see: "Connected: Browse pending..." and "Connecting: Download Mode"

Can i get a little assistance please?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 15, 2026, 3:17pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/11 "2026-09-15T15:17:35Z")

</div>

Download mode means some engineer or technician is messing with the PLC program.

---

<div class="post-metadata">

**Author:** ![Enrique\_Torres](https://avatars.discourse-cdn.com/v4/letter/e/ad7895/32.png) [@Enrique\_Torres](https://forum.inductiveautomation.com/u/Enrique_Torres)\
**Post date:** [September 15, 2026, 3:19pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/12 "2026-09-15T15:19:01Z")

</div>

oh wow...no one should have access to the PLC.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 15, 2026, 3:19pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/13 "2026-09-15T15:19:56Z")

</div>

If the PLC is power cycled, it might show that briefly before the program is initialized.

---

<div class="post-metadata">

**Author:** ![Enrique\_Torres](https://avatars.discourse-cdn.com/v4/letter/e/ad7895/32.png) [@Enrique\_Torres](https://forum.inductiveautomation.com/u/Enrique_Torres)\
**Post date:** [September 15, 2026, 3:22pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/14 "2026-09-15T15:22:50Z")

</div>

we upgraded from v7.9 to v8.3 and had issues, so then we went to v3.1 and that is where we are at now. The version upgrade was a year ago and then we went down for a water tank maintenance project. When we came back online, that is when I started getting the issue i described earlier ...i have not cycled power to the PLC.

---

<div class="post-metadata">

**Author:** ![Enrique\_Torres](https://avatars.discourse-cdn.com/v4/letter/e/ad7895/32.png) [@Enrique\_Torres](https://forum.inductiveautomation.com/u/Enrique_Torres)\
**Post date:** [September 15, 2026, 3:25pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/15 "2026-09-15T15:25:17Z")

</div>

Awesome, that gives me an area where i can go and start troubleshooting. sounds like it is a wiring/power issue, not a gateway issue.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 15, 2026, 4:16pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/16 "2026-09-15T16:16:51Z")

</div>

Is it stuck in download mode? Are you sure the PLC didn't lose its program after a power cycle? (Bad battery on old CPU, perhaps?)

---

<div class="post-metadata">

**Author:** ![Enrique\_Torres](https://avatars.discourse-cdn.com/v4/letter/e/ad7895/32.png) [@Enrique\_Torres](https://forum.inductiveautomation.com/u/Enrique_Torres)\
**Post date:** [September 15, 2026, 4:31pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/17 "2026-09-15T16:31:53Z")

</div>

i can see the PLC in RSLinx and i can go online in my laptop, but in one of our machines that is a client that has RSlinx and RSLogix 5000 in it, i lose connection when ever Ignition loses comms. so it comes and goes.  
it is only that one PLC.

 ![1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/e/ceec9d0f1691edb3ed9507a0dfff3824bc090fa5.jpeg)  
 ![2](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/e/ceec9d0f1691edb3ed9507a0dfff3824bc090fa5.jpeg)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 15, 2026, 5:15pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/18 "2026-09-15T17:15:05Z")

</div>

> [@Enrique\_Torres](#):
>
> RSLogix 5000 in it, i lose connection when ever Ignition loses comms

Then it is a problem in your network or in the hardware, not in Ignition.

---

<div class="post-metadata">

**Author:** ![Enrique\_Torres](https://avatars.discourse-cdn.com/v4/letter/e/ad7895/32.png) [@Enrique\_Torres](https://forum.inductiveautomation.com/u/Enrique_Torres)\
**Post date:** [September 15, 2026, 6:00pm UTC](https://forum.inductiveautomation.com/t/plc-ignition-connection-disconnected-protocol-eip-run-mode/97619/19 "2026-09-15T18:00:37Z")

</div>

i just thought since i can see it through my laptop i thought maybe it was in the Gateway. Awesome, thank you sir for your help, greatly appreciate 🤘