# PLC using Logix Driver goes "Idle"

**URL:** <https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505>\
**Category:** Ignition\
**Created:** [June 18, 2018, 12:14pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505 "2018-06-18T12:14:03Z")\
**Posts on this page:** 20\
**Page:** 2

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 25, 2020, 1:33pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/21 "2020-10-25T13:33:24Z")

</div>

I am having the same issue as well with a L8 series ControlLogix. This is my first Ignition HMI, so not real sure how to pull these logs, but I do know it seems to also possibly happen after a download to the PLC, or an existing PLC Controller tag name change. This is not every time an existing PLC tag name is changed I would like to note just trying to observer something that could be causing. Is there any information I could provide in helping to find a fix?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 25, 2020, 1:40pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/22 "2020-10-25T13:40:58Z")

</div>

If you or anyone else interesting in testing something are currently running 8.0.16 then you can install this module and report back if the issue is still happening or not: [https://www.dropbox.com/s/8lnfvnufjvh017z/OPC-UA-module.modl?dl=0](https://www.dropbox.com/s/8lnfvnufjvh017z/OPC-UA-module.modl?dl=0)

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 25, 2020, 1:51pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/23 "2020-10-25T13:51:01Z")

</div>

If I was to put this on my development laptop, would that mean I couldn’t push my _changes_ to the Live Server without installing it there as well?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 25, 2020, 2:07pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/24 "2020-10-25T14:07:59Z")

</div>

Do you mean like project changes for your Vision or Perspective?

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 25, 2020, 4:23pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/25 "2020-10-25T16:23:00Z")

</div>

Yes project and tag changes imported in.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 25, 2020, 4:26pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/26 "2020-10-25T16:26:42Z")

</div>

No it wouldn’t have any effect on that.

---

<div class="post-metadata">

**Author:** ![bkthomas](https://avatars.discourse-cdn.com/v4/letter/b/7ab992/32.png) [@bkthomas](https://forum.inductiveautomation.com/u/bkthomas)\
**Post date:** [October 26, 2020, 6:06pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/28 "2020-10-26T18:06:35Z")

</div>

I have also noticed it happening after a download to the PLC.  
During the download the device connection will go Idle, but then the gateway will not reconnect once the download has completed.

---

<div class="post-metadata">

**Author:** ![bkthomas](https://avatars.discourse-cdn.com/v4/letter/b/7ab992/32.png) [@bkthomas](https://forum.inductiveautomation.com/u/bkthomas)\
**Post date:** [October 26, 2020, 6:19pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/29 "2020-10-26T18:19:46Z")

</div>

Hi Kevin, we installed the module you provided and then tested doing another download into the PLC.  
The connection went Idle during download. and then successfully reconnected once the download was complete.

Whatever y’all fixed in the UA module seems to have done it. At least for that part. 😃 👍

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 26, 2020, 6:21pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/30 "2020-10-26T18:21:37Z")

</div>

Ok, thanks. This fix is already merged such that it will be in the 8.1.1 release and we’re going to backport for 8.0.17 as well.

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 26, 2020, 8:50pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/31 "2020-10-26T20:50:11Z")

</div>

I can confirm the same success with 8.0.17. Had it on my development laptop but not on server. Laptop with 8.0.17 successfully connected, while Live Server was in Idle state after a PLC download. Good job guys! Thanks for the quick fix! 👍

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 27, 2020, 5:06pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/32 "2020-10-27T17:06:02Z")

</div>

Sad to report, I have entered an Idle state again that required a disable/enable to get Device connected again. ☹

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 27, 2020, 5:07pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/33 "2020-10-27T17:07:52Z")

</div>

On your laptop where you installed the new module or on the server?

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 27, 2020, 5:09pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/34 "2020-10-27T17:09:20Z")

</div>

On the live HMI Server

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 27, 2020, 5:09pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/35 "2020-10-27T17:09:57Z")

</div>

Well I hate to ask a dumb question but did you install the new module on that server as well? You only mentioned installing it on your laptop.

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 27, 2020, 5:10pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/36 "2020-10-27T17:10:22Z")

</div>

Yes, my apologies I added it this morning after running all day yesterday with no problems on my laptop.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 27, 2020, 5:12pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/37 "2020-10-27T17:12:50Z")

</div>

Ok, if you can, leave all the loggers you find under `com.digitalpetri.enip` on TRACE level and get the logs if/when it happens again. Also set the logger for `drivers.LogixDriver.Requests.ReadBrowseHashRequest` to TRACE as well.

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 27, 2020, 10:38pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/38 "2020-10-27T22:38:33Z")

</div>

Sorry for the delay in response, but I am unaware on how to do these logs. I tried searching for the logs with that name but under the logs in the status tab of gateway but no luck. I will look into getting a better understanding of the logs and jut keep disabling/enabling for now.

---

<div class="post-metadata">

**Author:** ![patrick.bennett](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/patrick.bennett/32/43916_2.png) [@patrick.bennett](https://forum.inductiveautomation.com/u/patrick.bennett)\
**Post date:** [October 28, 2020, 11:56am UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/39 "2020-10-28T11:56:02Z")

</div>

I have enabled TRACE on the two logs. It appears I have two writes very frequently on the “…ReadBrowseHashRequest” but I am guessing that is normal?

---

<div class="post-metadata">

**Author:** ![bkthomas](https://avatars.discourse-cdn.com/v4/letter/b/7ab992/32.png) [@bkthomas](https://forum.inductiveautomation.com/u/bkthomas)\
**Post date:** [October 28, 2020, 12:57pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/40 "2020-10-28T12:57:42Z")

</div>

Yeahhh, we came back to the PLC being Idle again this morning. Seemingly just decided to take a nap and stop updating.  
I’ve enabled the logs to TRACE on our system as well.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 28, 2020, 1:12pm UTC](https://forum.inductiveautomation.com/t/plc-using-logix-driver-goes-idle/18505/41 "2020-10-28T13:12:37Z")

</div>

@bkthomas do you also have the new OPC UA module from earlier in this thread installed?