Ignition v7.2.5. PLC5/60 Ser.E Rev.B w/1785-ENET.

When monitoring a timer’s staus bits {Enable, Timing and Done}, the OPC item path of [device]Tx:x.DN works fine.

The OPC item path of [device]Tx:x.TT actually reports the status of the EN bit.

The OPC item path of [device]Tx:x.EN actually reports the status of the TT bit.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [May 9, 2011, 7:13pm UTC](https://forum.inductiveautomation.com/t/plc5-timer-status-bits/2925/2 "2011-05-09T19:13:19Z")

</div>

You are correct.

We’ll have it fixed in the next beta release.

Thank you,

Tom

---

<div class="post-metadata">

**Author:** ![taspencer](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/taspencer/32/60881_2.png) [@taspencer](https://forum.inductiveautomation.com/u/taspencer)\
**Post date:** [May 9, 2011, 7:32pm UTC](https://forum.inductiveautomation.com/t/plc5-timer-status-bits/2925/3 "2011-05-09T19:32:05Z")

</div>

Awesome! Thank you.