Has anyone used a Pro Soft MVI46-DFNT Ethernet I/P card to communicate to Ignition?  
Talking with Pro Soft they say It acts like a SLC 5/05 so would Ignitions SLC driver work with this card?

---

<div class="post-metadata">

**Author:** ![Kakkerlak](https://avatars.discourse-cdn.com/v4/letter/k/bb73d2/32.png) [@Kakkerlak](https://forum.inductiveautomation.com/u/Kakkerlak)\
**Post date:** [March 8, 2012, 4:34pm UTC](https://forum.inductiveautomation.com/t/pro-soft-card-with-allen-bradley-slc-5-03/4118/2 "2012-03-08T16:34:20Z")

</div>

I’m not sure you’ll find somebody who has done precisely that, but I expect it to work. The “DFNT” modules have a fairly thorough implementation of the PLC or SLC communication instruction set.

In fact, I believe that Prosoft got permission to actually respond to identity queries with the SLC-5/05 or PLC-5E’s Identity objects, just with a program name string identifying itself as a Prosoft Module.

The big question I would have is whether or not the DFNT module responds correctly to a “List Data Tables” request, which is what Ignition OPC-UA or RSLinx uses to determine which data tables to show in a browse.

Remember that with a Prosoft card you’re not actually accessing the data tables inside the SLC controller, but rather the 5000-word flat file Database inside the MVI module, which emulates a set of SLC data tables.

If you wanted actual access to the data tables of the controller, you’ll want to use a 1761-NET-ENI or Digi One IAP.

---

<div class="post-metadata">

**Author:** ![everardohr](https://avatars.discourse-cdn.com/v4/letter/e/e56c9b/32.png) [@everardohr](https://forum.inductiveautomation.com/u/everardohr)\
**Post date:** [August 7, 2013, 11:05pm UTC](https://forum.inductiveautomation.com/t/pro-soft-card-with-allen-bradley-slc-5-03/4118/3 "2013-08-07T23:05:39Z")

</div>

Does anyone have confirmation in this setup?  
I have one module and I am able to connect using RSLinx OPC client, but if I try to connect using SLC5/05 Ethernet driver I keep receiving a Config Error Quality status on the configured tag.

Using Ignition 7.6.2.