Hi  
I am trying to connect with OPC SERVER  
in a remote computer via TCP-IP  
and i am receveing this fault message  
com.jniwrapper.win32.com.ComException: COM object method returns error code: 0x80070005; E\_ACCESSDENIED (Access is denied.)  
com.jniwrapper.win32.com.ComException.checkResult(SourceFile:172)  
com.jniwrapper.win32.com.ComFunctions.coCreateInstanceEx(SourceFile:229)  
com.inductiveautomation.opccom.COMServerImpl$ConnectServerJob.internalRun(COMServerImpl.java:633)  
com.inductiveautomation.opccom.wrapper.OleJob.run(OleJob.java:45)  
com.jniwrapper.win32.MessageLoopThread$ThreadSynchronizedAction.run(MessageLoopThread.java:566)  
com.jniwrapper.win32.MessageLoopThread$LoopThread.run(MessageLoopThread.java:508)

Please Somebody can help me ?  
Best regards  
Thanks  
Victor

---

<div class="post-metadata">

**Author:** ![Colby.Clegg](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/colby.clegg/32/3282_2.png) [@Colby.Clegg](https://forum.inductiveautomation.com/u/Colby.Clegg)\
**Post date:** [February 16, 2010, 5:36pm UTC](https://forum.inductiveautomation.com/t/problem-instaling-ignition-in-remote-server/1545/2 "2010-02-16T17:36:36Z")

</div>

Hi,

Looks like you’re just running into the standard DCOM security issues that can make these types of connections a bit tricky. I recommend searching the forum or the internet in general for information about DCOM security settings. [This post](http://www.inductiveautomation.com/forum/viewtopic.php?f=25&t=2259), in the Knowledge Base forum, is a good place to start.

Which OPC server are you using? I only ask because Kepware has released version 5.2, which supports UA and will let you avoid COM/DCOM entirely. At any rate, take a shot at getting the DCOM security settings set up, and post back if you have any problems.

Regards,