# Problem reading tags from Siemens S7-1500 PLC

**URL:** <https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244>\
**Category:** Ignition\
**Created:** [November 3, 2020, 3:55pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244 "2020-11-03T15:55:59Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![luis.3.flores](https://avatars.discourse-cdn.com/v4/letter/l/8491ac/32.png) [@luis.3.flores](https://forum.inductiveautomation.com/u/luis.3.flores)\
**Post date:** [November 3, 2020, 3:55pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/1 "2020-11-03T15:55:59Z")

</div>

I am having an issue trying to read the tags from a PLC S7-1500.  
I have access level set as “Full access (no protection” and the connection mechanism enabled for “permit access with PUT/GET communications from remote partner”.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/6/d677cccfd7ed63cdc4428f11565d1007fab86eaa.png)

I am using the Ignition driver for S7-1500 over ethernet and the PLC is connected.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/d/dd2a019a33e055ec5f2197709b8cc065835cbfd2.png)  
On the designer I added an OPC tag named [s71500]DB66,STRING44.20 so I can read the following tag:  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/5/b53256b99cd21a416b07eb977abc693c31ffecd4.png)

I get error 8104 on the logs.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/a/baa4df427be5db7dd1de1b4298642b00d2565f5c.png)

Any idea what is wrong ?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 3, 2020, 3:57pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/2 "2020-11-03T15:57:29Z")

</div>

Have you disabled optimized access for the data block(s) you are trying to read?

---

<div class="post-metadata">

**Author:** ![luis.3.flores](https://avatars.discourse-cdn.com/v4/letter/l/8491ac/32.png) [@luis.3.flores](https://forum.inductiveautomation.com/u/luis.3.flores)\
**Post date:** [November 3, 2020, 3:58pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/3 "2020-11-03T15:58:12Z")

</div>

Yes.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/1/2128046faafda51a12ae8f614468322524810c5c.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 3, 2020, 4:07pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/4 "2020-11-03T16:07:07Z")

</div>

Hmm. No further idea. @chi or @zxcslo are the go-to guys for Siemens.

ps. Start new topics in the future. Necromancy is not always noticed by those who might be able to help.

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [November 3, 2020, 5:06pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/5 "2020-11-03T17:06:50Z")

</div>

Well… the error 8104 means that access to the address is not allowed. So there must be something with the “Permit access with PUT/GET…” in the HW configuration of the PLC.  
Can you try to compile the PLC program again and download it to the PLC?  
Is this (STRING) the only tag you can’t read?

---

<div class="post-metadata">

**Author:** ![luis.3.flores](https://avatars.discourse-cdn.com/v4/letter/l/8491ac/32.png) [@luis.3.flores](https://forum.inductiveautomation.com/u/luis.3.flores)\
**Post date:** [November 3, 2020, 5:18pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/6 "2020-11-03T17:18:46Z")

</div>

I cannot read any tag at all. I will try to compile and download it again.

---

<div class="post-metadata">

**Author:** ![luis.3.flores](https://avatars.discourse-cdn.com/v4/letter/l/8491ac/32.png) [@luis.3.flores](https://forum.inductiveautomation.com/u/luis.3.flores)\
**Post date:** [November 3, 2020, 5:44pm UTC](https://forum.inductiveautomation.com/t/problem-reading-tags-from-siemens-s7-1500-plc/40244/7 "2020-11-03T17:44:56Z")

</div>

I compiled the hardware configuration again and downloaded and it is working now! Thanks a lot!