Hello there,

i tried to set up a simple communication in my local network that involve an Allen-Bradley PLC, Ignition v8.0.6 STABLE and Kepware.  
I'm trying to read Tags as fast as i can, ergo 100/150ms.

The PLC routine has 1 counter that increments my integer by 1 every 100ms, but in Ignition i'm unable to see those changes (it goes barely around 400/500ms).

My Project settings:

> 1. The TAG (ignition side) has a **Leased Tag-Group** that is set to **0 poll rate when not requested** and **100ms when requested**.

> 1. **Project Properties \> General \> Client poll rate:** 100ms

> 1. **Project Properties \> Timing \> Polling Base Rate:** 200ms (because we can't go lower?)

> 1. The page has **only 1 Numeric Label**.

Here is a video: Link

Is it even possible to reach this speed? I feel like something is slow, or i'm handling it in the wrong way.  
Thanks for your future help.

N.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [December 16, 2019, 3:41pm UTC](https://forum.inductiveautomation.com/t/question-ignition-kepware-tags-value-speed/30732/2 "2019-12-16T15:41:39Z")

</div>

Hmm. You can’t really expect to see every change because you’re dealing with so many overlapping polling cycles here (kepware polling PLC, OPC subscription evaluation, ignition client/designer polling gateway), but that’s looking a little slower than I’d expect. Let me poke around a bit and see if I can get a better result.

In the meantime, you should verify (somehow? not sure) that Kepware is actually able to poll at 100ms. With only 1 tag and nothing else subscribed it shouldn’t be an issue, but if you’re using a PLC with a heavy comm load from other systems maybe not.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [December 16, 2019, 9:16pm UTC](https://forum.inductiveautomation.com/t/question-ignition-kepware-tags-value-speed/30732/3 "2019-12-16T21:16:37Z")

</div>

Hey, it looks like there’s a hardcoded 250ms debounce happening somewhere between the gateway and client/designer comms.

For the purposes of alarming, history, tag changes, etc… you should be getting your updates at the requested rate, but for display purposes in client/designer right now you won’t see updates faster than 250ms.

I’m going to look into either removing this or some other fix.

---

<div class="post-metadata">

**Author:** ![n.meluccio](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/n.meluccio/32/4858_2.png) [@n.meluccio](https://forum.inductiveautomation.com/u/n.meluccio)\
**Post date:** [December 17, 2019, 7:18am UTC](https://forum.inductiveautomation.com/t/question-ignition-kepware-tags-value-speed/30732/4 "2019-12-17T07:18:35Z")

</div>

Ok, thank you for the explanation Kevin.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 17, 2019, 11:09am UTC](https://forum.inductiveautomation.com/t/question-ignition-kepware-tags-value-speed/30732/5 "2019-12-17T11:09:26Z")

</div>

> [@Kevin.Herron](#):
>
> Hey, it looks like there’s a hardcoded 250ms debounce happening somewhere between the gateway and client/designer comms.

Uhm, project setting for polling?

---

<div class="post-metadata">

**Author:** ![n.meluccio](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/n.meluccio/32/4858_2.png) [@n.meluccio](https://forum.inductiveautomation.com/u/n.meluccio)\
**Post date:** [December 17, 2019, 2:07pm UTC](https://forum.inductiveautomation.com/t/question-ignition-kepware-tags-value-speed/30732/6 "2019-12-17T14:07:08Z")

</div>

I made another test, and it looks like that TAGs defined in Ignition are very slow.

What i tried:

> I'm reading 10 values from different OPC addresses (system.opc.readValues) every 100ms by using a "Timer component". Whenever the timer value change, it runs a script that reads those paths and put them into the related numeric label.

Here is the video showing that it's MUCH BETTER with the timer: Link

Cheers,  
N.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [December 17, 2019, 2:19pm UTC](https://forum.inductiveautomation.com/t/question-ignition-kepware-tags-value-speed/30732/7 "2019-12-17T14:19:46Z")

</div>

No, something new in 8.0 that’s actually hardcoded.