# Read Ignition tags from PLC

**URL:** <https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472>\
**Category:** Ignition\
**Created:** [November 14, 2022, 2:55pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472 "2022-11-14T14:55:37Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![Nathan\_Higgins1](https://avatars.discourse-cdn.com/v4/letter/n/8797f3/32.png) [@Nathan\_Higgins1](https://forum.inductiveautomation.com/u/Nathan_Higgins1)\
**Post date:** [November 14, 2022, 2:55pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/1 "2022-11-14T14:55:37Z")

</div>

How do I read Ignition tags from an external device? I have a HMI that needs to read tags out of my ignition project

---

<div class="post-metadata">

**Author:** ![kcollins](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kcollins/32/19646_2.png) [@kcollins](https://forum.inductiveautomation.com/u/kcollins)\
**Post date:** [November 14, 2022, 3:16pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/2 "2022-11-14T15:16:41Z")

</div>

You can connect OPC-UA clients to Ignition's OPC-UA server by adjusting the bind address (default is `localhost`). You can enable "Expose Tag Providers" in the [OPC-UA Server Settings](https://docs.inductiveautomation.com/display/DOC81/Ignition%27s+OPC+UA+Server) to make Ignition tag providers visible via the OPC-UA interface.

Keep in mind, however, that tag security settings are **not** enforced on the _Devices_ folder within the Ignition OPC-UA server which will be accessible in addition to the tag providers themselves. If you've got devices configured on this gateway, clients will be able to read/write to device tags directly in the OPC-UA server.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 14, 2022, 3:18pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/3 "2022-11-14T15:18:55Z")

</div>

There are a couple options:

- Enable the Ignition OPC Server's Expose Tags feature. This is a global setting, and requires you to set tag security everywhere you _don't_ want something exposed.

- Run an OPC driver that acts as a protocol server. I happen to have modules that offer two choices: [Logix-style EtherNet/IP](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-ethernetip-class-1-communications) and [Modbus](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-advanced-modbus). In these cases, you explicitly connect tags to OPC items in these servers, and the HMI can use that protocol to read/write those values.

{ /shameless plug }

---

<div class="post-metadata">

**Author:** ![Nathan\_Higgins1](https://avatars.discourse-cdn.com/v4/letter/n/8797f3/32.png) [@Nathan\_Higgins1](https://forum.inductiveautomation.com/u/Nathan_Higgins1)\
**Post date:** [November 14, 2022, 5:41pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/4 "2022-11-14T17:41:00Z")

</div>

I'm pretty new to Ignition, what would I set the bind address to?

---

<div class="post-metadata">

**Author:** ![kcollins](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kcollins/32/19646_2.png) [@kcollins](https://forum.inductiveautomation.com/u/kcollins)\
**Post date:** [November 14, 2022, 6:04pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/5 "2022-11-14T18:04:03Z")

</div>

With the default of `localhost`, Ignition itself is allowed to make a loopback connection to the OPC-UA server. If you were to set it to `0.0.0.0`, this would enable connections from all network interfaces (versus just the loopback adapter). Also note that making changes to OPC-UA Server configuration requires you to restart the OPC-UA module--I mention this because it is one area that is somewhat different than other typical settings that are immediately recognized upon _Save_.

---

<div class="post-metadata">

**Author:** ![Nathan\_Higgins1](https://avatars.discourse-cdn.com/v4/letter/n/8797f3/32.png) [@Nathan\_Higgins1](https://forum.inductiveautomation.com/u/Nathan_Higgins1)\
**Post date:** [November 14, 2022, 6:12pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/6 "2022-11-14T18:12:11Z")

</div>

would I leave the local host in there and add 0.0.0.0 after a comma  
?

---

<div class="post-metadata">

**Author:** ![kcollins](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kcollins/32/19646_2.png) [@kcollins](https://forum.inductiveautomation.com/u/kcollins)\
**Post date:** [November 14, 2022, 6:24pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/7 "2022-11-14T18:24:01Z")

</div>

You'd just replace `localhost` with `0.0.0.0` to bind to all network interfaces instead of just the loopback adapter.

---

<div class="post-metadata">

**Author:** ![Nathan\_Higgins1](https://avatars.discourse-cdn.com/v4/letter/n/8797f3/32.png) [@Nathan\_Higgins1](https://forum.inductiveautomation.com/u/Nathan_Higgins1)\
**Post date:** [November 14, 2022, 7:19pm UTC](https://forum.inductiveautomation.com/t/read-ignition-tags-from-plc/66472/8 "2022-11-14T19:19:05Z")

</div>

I will give that a try, thanks