# Read plc tag value to tag history

**URL:** <https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301>\
**Category:** Ignition\
**Created:** [December 8, 2020, 4:45pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301 "2020-12-08T16:45:42Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [December 8, 2020, 4:45pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/1 "2020-12-08T16:45:42Z")

</div>

Hello, I am trying to read analog value from control Logix plc to the tag history, my requirement is to catch values between each 300ms in ignition for the analog sensor value. In the tag history, I enabled the tag history, and change the min time to 300ms. However, I can only see the value for each 10-12 sec.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/d/fdc7422ce983ecf9892f3173d7a0c3e1df672e40.png)

Is there anything I miss or anything else i should do? thanks ahead for any suggestion!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 8, 2020, 4:51pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/2 "2020-12-08T16:51:10Z")

</div>

You will have to put the tag in a tag group that _reads_ that fast, before you can _store_ that fast. Adjust the interval for your tag group (or probably create a new tag group just for the tag that runs this fast). The default read interval is one second, and the default storage policy is to store on change. You will have to set the **maximum** time to 300ms.

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [December 8, 2020, 5:20pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/3 "2020-12-08T17:20:23Z")

</div>

Thank you so much, my problem was exactly what you mentioned, I did not configure the reading part. Thank you!

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 3:59pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/4 "2021-02-26T15:59:26Z")

</div>

Hello,  
I am running into a problem that somehow my data start to read every 9 second from plc while I am still putting the data in a tag group of executing each 300ms. I believe there is nothing has been changed. Is there anything that could influence this? thanks!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 26, 2021, 4:08pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/5 "2021-02-26T16:08:35Z")

</div>

Did you add more tags in Ignition subscribed to that same Logix PLC? That could/would slow down any other tags. Older Logix PLCs also shared CPU time between tasks and communications: are there program changes in the PLC that would reduce available comms time?

FWIW, I don’t think you are likely to have satisfactory results with sub-second recording intervals with anything built on a query-response driver. (Like Ignition’s standard Logix drivers.) Such high speed tasks are precisely why I created my I/O-based [Ethernet/IP Class 1 Communications](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-ethernetip-class-1-communications) module. You should consider re-designing your application to use an appropriate high-performance protocol.

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 4:53pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/6 "2021-02-26T16:53:49Z")

</div>

Hello

Thank you for your advises, I did change things in PLC beforehand. However, right now I have changed back to before stage and have even less program that before, I still have the same issue. Is there anything that I should look at more? thanks!

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 4:58pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/7 "2021-02-26T16:58:14Z")

</div>

I do believe it might relate to the change I made, but I changed it back, I still have the same issue.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 26, 2021, 5:04pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/8 "2021-02-26T17:04:35Z")

</div>

What does the device diagnostics page in the Ignition gateway for this device look like?

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 5:14pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/9 "2021-02-26T17:14:57Z")

</div>

I see the load factor at 1000ms schedule is 700%, is this the issue?

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 5:17pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/10 "2021-02-26T17:17:19Z")

</div>

but the graph shows that all are generally finish less than 300ms

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 26, 2021, 5:18pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/11 "2021-02-26T17:18:15Z")

</div>

Yes, that’s probably the issue. Can you post some screenshots of that whole section?

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 5:20pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/12 "2021-02-26T17:20:37Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/9/f95563e0ae2b6e5c0f133013a163a7c7a99bb736.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 26, 2021, 5:22pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/13 "2021-02-26T17:22:59Z")

</div>

Yeah, so, you’re requesting too much data too quickly and the device can’t keep up.

You can try messing with the Concurrent Requests and CIP Connection Size settings a little bit.

If there are only a handful of tags you need at a really fast rate and the rest can be slow then you could also move these to their own device connection that you use only for these tags so that they aren’t stuck waiting for the 400+ other requests that the driver is dealing with to service all the other tags you have subscribed.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 26, 2021, 5:32pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/14 "2021-02-26T17:32:35Z")

</div>

Those are horribly slow response times. Logix should be responding in single digit milliseconds.

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 5:33pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/15 "2021-02-26T17:33:47Z")

</div>

Thank you I got this fix by temporarily remove a big chunk of opc tags. But one interesting thing is that I have exactly tags in another ControlLogix drivers and they are working fine, but in this logix driver, I have the issue like this. Is this because of the different drivers?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 26, 2021, 5:34pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/16 "2021-02-26T17:34:47Z")

</div>

> [@mbai1](#):
>
> but in this logix driver, I have the issue like this. Is this because of the different drivers?

Yes, that's part of it. What firmware version is the device?

Rockwell disabled direct memory access starting in 20.19 and introduced a new "API" for accessing tags in v21+. It is not as fast as the old DMA method.

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 5:38pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/17 "2021-02-26T17:38:23Z")

</div>

we are using 30.011

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 26, 2021, 5:39pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/18 "2021-02-26T17:39:31Z")

</div>

I think you are using the wrong driver, based on your logger name.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 26, 2021, 5:39pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/19 "2021-02-26T17:39:49Z")

</div>

Then you must use the newer Logix driver.

But still, the response times should be single-digit milliseconds as @pturmel suggested. So either a bunch of other stuff is talking to the device as well or your network is b0rked. Or the comms load is just saturated.

edit: yeah, your screenshot has logs from a legacy driver… those are either there by mistake or you’re looking at a legacy driver hooked up to a PLC that cannot be running v30.11.

---

<div class="post-metadata">

**Author:** ![mbai1](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@mbai1](https://forum.inductiveautomation.com/u/mbai1)\
**Post date:** [February 26, 2021, 5:44pm UTC](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301/20 "2021-02-26T17:44:45Z")

</div>

the logger:contrologixDriver was for something else, not the one we are talking about

[Next page](https://forum.inductiveautomation.com/t/read-plc-tag-value-to-tag-history/41301.md?page=2)