That’s going to be much slower than requesting only each top level structured value instead, at least if you are using the OPC UA server built in to the S7-1500.

When reading a structured value it will be received in Ignition as a JSON object, containing all the member values and any member structs as embedded JSON objects modeled the same way.

---