# Red Lion Datastation Modubus TCP Conectivity

**URL:** <https://forum.inductiveautomation.com/t/red-lion-datastation-modubus-tcp-conectivity/9914>\
**Category:** General Discussion\
**Created:** [April 15, 2015, 5:27am UTC](https://forum.inductiveautomation.com/t/red-lion-datastation-modubus-tcp-conectivity/9914 "2015-04-15T05:27:51Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![0sm0](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/0sm0/32/15228_2.png) [@0sm0](https://forum.inductiveautomation.com/u/0sm0)\
**Post date:** [April 15, 2015, 5:27am UTC](https://forum.inductiveautomation.com/t/red-lion-datastation-modubus-tcp-conectivity/9914/1 "2015-04-15T05:27:51Z")

</div>

Hey Guys,

Wondering if anybody has connected Ignition to a Red Lion Datastation via Modbus TCP successfully before?

Using a Modbus TCP driver I get Ignition cycling between “Connected” and “Disconnected”

Red Lion Network Protocol set to Modbus TCP/IP slave

No Doubt I am missing some settings somewhere??

Cheers for any pointers

Tim…

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 15, 2015, 3:02pm UTC](https://forum.inductiveautomation.com/t/red-lion-datastation-modubus-tcp-conectivity/9914/2 "2015-04-15T15:02:53Z")

</div>

Have you defined any tags yet? Cycling between connected and disconnected usually happens when the device closes the connection due to inactivity.

---

<div class="post-metadata">

**Author:** ![0sm0](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/0sm0/32/15228_2.png) [@0sm0](https://forum.inductiveautomation.com/u/0sm0)\
**Post date:** [April 22, 2015, 2:05am UTC](https://forum.inductiveautomation.com/t/red-lion-datastation-modubus-tcp-conectivity/9914/3 "2015-04-22T02:05:38Z")

</div>

Many Thanks,

Apparently the tags I had Mapped in Ignition were not correctly lining up with the tag mapping through the Datastation to the PLC.

Cheers