# Redundant system OPC problem

**URL:** <https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807>\
**Category:** Ignition\
**Created:** [March 17, 2017, 7:18pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807 "2017-03-17T19:18:44Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![roshanbhosale](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/roshanbhosale/32/4899_2.png) [@roshanbhosale](https://forum.inductiveautomation.com/u/roshanbhosale)\
**Post date:** [March 17, 2017, 7:18pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/1 "2017-03-17T19:18:44Z")

</div>

Hi everyone,  
I am using ignition’s reduntant system architecture in one of my project.  
I have configured an OPC server in one of the machine which acts as ignition master as well in redundant system.  
but the problem is when i configure the redundant client of ignition in other machine it gives me error for the OPC connection.  
since i have installed the OPC server in ignition master system locally, i have configured the OPC-UA server as locally available .Now when i try to change the setting of OPC server in backup system (setting IP address of the OPC server location) it does not allow me.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 17, 2017, 7:42pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/2 "2017-03-17T19:42:46Z")

</div>

What version are you on? At some point there was an additional group of settings added to the OPC UA connections where you could specify the discovery, endpoint, and host override that would be used if the currently running gateway was the redundant backup. They should be under the “Redundancy” category.

---

<div class="post-metadata">

**Author:** ![roshanbhosale](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/roshanbhosale/32/4899_2.png) [@roshanbhosale](https://forum.inductiveautomation.com/u/roshanbhosale)\
**Post date:** [March 18, 2017, 4:56am UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/3 "2017-03-18T04:56:59Z")

</div>

i am using ignition 7.8.4 version

---

<div class="post-metadata">

**Author:** ![roshanbhosale](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/roshanbhosale/32/4899_2.png) [@roshanbhosale](https://forum.inductiveautomation.com/u/roshanbhosale)\
**Post date:** [March 19, 2017, 5:22pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/4 "2017-03-19T17:22:24Z")

</div>

![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/b/b05dcdccfedcb06c151062d8fda36d10c94ebcee.jpg)

Find the attached image. here there is no option of endpoint setting. then how to set the redundancy for this OPC server for redundant gateway node.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 20, 2017, 2:59pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/5 "2017-03-20T14:59:18Z")

</div>

Are you trying to achieve redundancy for the OPC COM connection?

---

<div class="post-metadata">

**Author:** ![roshanbhosale](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/roshanbhosale/32/4899_2.png) [@roshanbhosale](https://forum.inductiveautomation.com/u/roshanbhosale)\
**Post date:** [March 20, 2017, 6:16pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/6 "2017-03-20T18:16:15Z")

</div>

Yes… is it possible?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 20, 2017, 6:20pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/7 "2017-03-20T18:20:03Z")

</div>

You’ll need to have the server running on the backup machine as well. There’s no way to point it at the master machine separately.

---

<div class="post-metadata">

**Author:** ![roshanbhosale](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/roshanbhosale/32/4899_2.png) [@roshanbhosale](https://forum.inductiveautomation.com/u/roshanbhosale)\
**Post date:** [March 22, 2017, 10:10am UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/8 "2017-03-22T10:10:54Z")

</div>

If I install OPC server in backup machine as well, then will redundancy will take place between them? Same OPC com servers installed seperately on two machines will have same Progid or different?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 22, 2017, 1:19pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/9 "2017-03-22T13:19:19Z")

</div>

Whether or not they have any concept of redundancy or even the same ProgId would be entirely dependent on the server. I would guess most could end up with the same ProgId but will run independent of each other.

---

<div class="post-metadata">

**Author:** ![roshanbhosale](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/roshanbhosale/32/4899_2.png) [@roshanbhosale](https://forum.inductiveautomation.com/u/roshanbhosale)\
**Post date:** [March 23, 2017, 6:07am UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/10 "2017-03-23T06:07:39Z")

</div>

Thank you Kevin.Herron for your reply. will check this thing with the vendor of OPC server supplier.

---

<div class="post-metadata">

**Author:** ![jose.granero](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jose.granero/32/11190_2.png) [@jose.granero](https://forum.inductiveautomation.com/u/jose.granero)\
**Post date:** [June 2, 2017, 5:28pm UTC](https://forum.inductiveautomation.com/t/redundant-system-opc-problem/12807/11 "2017-06-02T17:28:25Z")

</div>

One question, in case I have a redundant configuration like the one suggested, two redundant gateways and two OPC DA servers running on both , the master and the secondary server, will Ignition redundancy manage the failure of the OPC server changing to the backup node?