Hi all,

I am running into an issue when importing changes to tags. If a tags alarm priority is changed, but the alarm is currently active, the alarm will remain the old priority until the alarm is cleared. I am looking for a way to have the alarm remain active, but update to the new priority.

Is it possible to refresh all the alarms?

I can programmatically disable, then re-enable all of the active alarms. But this leaves an override on UDT tags enabled property.

Any suggestions to this problem are appreciated.

---

<div class="post-metadata">

**Author:** ![MMaynard](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mmaynard/32/3366_2.png) [@MMaynard](https://forum.inductiveautomation.com/u/MMaynard)\
**Post date:** [October 21, 2025, 5:01pm UTC](https://forum.inductiveautomation.com/t/refresh-alarm-priority-after-tag-import/111623/2 "2025-10-21T17:01:10Z")

</div>

I don’t think you can do that with keeping the alarm in the active state.

I usually just right click, restart tag to get the updated alarm information.