I’m trying to setup a Hub and Spoke architecture where, from the Hub I can view the Tags configured at the Spoke. Ignition is installed at both the Hub (Central Site) and the Spoke (Remote Site). At the spoke I have a number of connected Devices (PLCs) and I’ve created a number of OPC Tags from these devices. I’ve also created a number of Query Tags and Expression Tags. I would like to see these Tags at the Hub. Is there any way I can do this easily?

This is what I’ve tried so far:  
At the Hub I’ve setup an OPC-UA connection to ignition at the Spoke. Using this I can see the connected devices at the Spoke, but I cannot see the Tags that have been configured in Ignition. I could Export all the tags at the spoke and import them into the Hub. This would replicate the OPC Tags, and expression tags, but to get the Query Tags working I need to make additional Database Connections.

Is there a way to just view the Tags at the Spoke directly?

Thanks,  
David

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [April 9, 2015, 11:20am UTC](https://forum.inductiveautomation.com/t/remote-tags/9893/2 "2015-04-09T11:20:12Z")

</div>

In the spoke configuration, go to OPC-UA → Settings  
– Check on “Expose Tag Providers”, then save.

 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/81845ba4f76a6531f079fe4260ffe094c0e37f4c.png)  

In the hub, you can now see the spoke,s tags through the OPC Browser  
 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/6/6042ccbdbb0ca55894013406d825e34525172e96.png)

---

<div class="post-metadata">

**Author:** ![DavidWisely](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/davidwisely/32/10482_2.png) [@DavidWisely](https://forum.inductiveautomation.com/u/DavidWisely)\
**Post date:** [April 9, 2015, 11:37am UTC](https://forum.inductiveautomation.com/t/remote-tags/9893/3 "2015-04-09T11:37:59Z")

</div>

Perfect!  
Thanks Jordan.