# Repeat an alarm mail notification every day

**URL:** <https://forum.inductiveautomation.com/t/repeat-an-alarm-mail-notification-every-day/25283>\
**Category:** Ignition\
**Created:** [May 24, 2019, 7:52am UTC](https://forum.inductiveautomation.com/t/repeat-an-alarm-mail-notification-every-day/25283 "2019-05-24T07:52:43Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![rea\_21](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/rea_21/32/7999_2.png) [@rea\_21](https://forum.inductiveautomation.com/u/rea_21)\
**Post date:** [May 24, 2019, 7:52am UTC](https://forum.inductiveautomation.com/t/repeat-an-alarm-mail-notification-every-day/25283/1 "2019-05-24T07:52:43Z")

</div>

Hi all,  
I have a Data Types with 6 tags all of them related with an alarm with mail notification (It sends a mail if the value stay under treshold for more than 2 hours).  
It works fine, but one of this alarm stay High for a lot of days and **I need to send a reminder to users every 24 hours (if the alarm is always high obviously).**  
It deals with a filter in a circuit (so physically, if you don’t clean the filter, the alarm can’t go low).  
I can I set this condition?  
Thank you

---

<div class="post-metadata">

**Author:** ![Brian](https://avatars.discourse-cdn.com/v4/letter/b/97f17d/32.png) [@Brian](https://forum.inductiveautomation.com/u/Brian)\
**Post date:** [May 24, 2019, 5:44pm UTC](https://forum.inductiveautomation.com/t/repeat-an-alarm-mail-notification-every-day/25283/2 "2019-05-24T17:44:12Z")

</div>

You can setup a separate alarm pipeline for this type of alarm. Have a look at [this page.](https://docs.inductiveautomation.com/display/DOC79/Pipeline+-+Simple+Loop)

---

<div class="post-metadata">

**Author:** ![rea\_21](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/rea_21/32/7999_2.png) [@rea\_21](https://forum.inductiveautomation.com/u/rea_21)\
**Post date:** [May 27, 2019, 7:42am UTC](https://forum.inductiveautomation.com/t/repeat-an-alarm-mail-notification-every-day/25283/3 "2019-05-27T07:42:47Z")

</div>

Thank you for your help, but this solution is the same to set this part in alarming configuration?

 ![delay](https://us1.discourse-cdn.com/inductiveautomation/original/2X/7/7b9eb1e6ddd96cd5936624e846c641e70f4cac71.jpeg)

---

<div class="post-metadata">

**Author:** ![Brian](https://avatars.discourse-cdn.com/v4/letter/b/97f17d/32.png) [@Brian](https://forum.inductiveautomation.com/u/Brian)\
**Post date:** [May 27, 2019, 3:30pm UTC](https://forum.inductiveautomation.com/t/repeat-an-alarm-mail-notification-every-day/25283/4 "2019-05-27T15:30:07Z")

</div>

Yes, those settings would be the same. Those tell ignition when the alarm should be active. The pipeline is what tells ignition to do about an active alarm.