Sounds like you’ve a few problems, perhaps some unrelated to the upgrade?

1. Logix driver overload:

> [@tebright1](#):
>
> I had a new issue with the Logix driver causing an overload

Lots of info to help with this problem over here (tip - wait to click the link until you’ve time to read the entire thread)…

> [@Ignition & Logix Best Practice Tips for better communications](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386):
>
> Hi All, After a whole bunch of issues I have gone down the rabbit hole of what is wrong with our setup on site. I will preface this by saying I a relatively new to all of this.... so be gentle stuck_out_tongue Based on much reading(such wow) I believe I have a list of things our site could take away for a better system. Some of them are easy to implement, whilst some of them need... significant work to realize. Especially the AOI approach in point 5 expressionless Before going too far a…

1. Historical data retention:

> [@tebright1](#):
>
> we needed the increase in historical buffer. From 7 days to 35

Note that Ignition Edge is also limited by the number of rows of data that you’re collecting (at time of writing, I believe the limit is 10M). To check your current data collection, head over to your Edge gateway config webpage, then “Status” –\> “Connections” –\> “Store and Forward” –\> “-Historian-” –\> “Details”. Under “Local Storage”, you should an indication of “-used- / -total- Records”. If -used- is \>= -total-, then you do not have 35 days of retention.

1. Edge –\> Full Sync Services

> [@tebright1](#):
>
> historian does not seem to be updating

What metric are you using to gauge that the Historian is not updating? If the metrics from #2 are updating, then Edge should be collecting & historizing the data. If Full gateway is unable to see those records being periodically sync’d, then there should be some breadcrumbs for additional troubleshooting in the logs (start on Edge @ “Status” –\> “Diagnostics” –\> “Logs”).

---