# Replaced PC running edge and now I cannot view my edge tags from my central gateway

**URL:** <https://forum.inductiveautomation.com/t/replaced-pc-running-edge-and-now-i-cannot-view-my-edge-tags-from-my-central-gateway/61973>\
**Category:** Ignition\
**Created:** [July 15, 2022, 7:24pm UTC](https://forum.inductiveautomation.com/t/replaced-pc-running-edge-and-now-i-cannot-view-my-edge-tags-from-my-central-gateway/61973 "2022-07-15T19:24:02Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![jrod](https://avatars.discourse-cdn.com/v4/letter/j/e480ec/32.png) [@jrod](https://forum.inductiveautomation.com/u/jrod)\
**Post date:** [July 15, 2022, 7:24pm UTC](https://forum.inductiveautomation.com/t/replaced-pc-running-edge-and-now-i-cannot-view-my-edge-tags-from-my-central-gateway/61973/1 "2022-07-15T19:24:02Z")

</div>

I have a few edge gateways setup on some PCs, they are all setup as realtime tag providers to a central gateway. After upgrading one of the edge PCs I can no longer view or edit the tags from my central gateway. I have gone through the gateway network settings on both ends and approved the certificates from the new PC.

My swap process was to create a gateway backup on the old edge PC, transfer the license then restore the gateway backup to the new edge PC, approve the new gateway network connections . Are there some steps I am missing to get this connection restored?

Right now when I am in the designer in a central project under the tag browser when I click the dropdown and select this edge provider I get an error “com.inductiveautomation.ignition.client.gateway\_interface.GatewayException: java.lang.SecurityException: Security settings do not allow access to tag provider ‘edge’.”

I have tried disabling the edge provider at my central gateway and re-enabling it. When I disable the edge provider from my Central gateways realtime tag providers it disappears from my central tag browser dropdown and shows up when I re-enable it so that seems to be working. Should I delete the edge tag provider on my central gateway and re-create it? The naming convention is the exact same so I don’t think I should have to do this. On my edge gateway the ‘service security’ default policy has been modified so in the tag access section I have everything set to ‘ReadWriteEdit’ and this configuration had been running for months on the old PC.

Any ideas? TIA

---

<div class="post-metadata">

**Author:** ![witman](https://avatars.discourse-cdn.com/v4/letter/w/d2c977/32.png) [@witman](https://forum.inductiveautomation.com/u/witman)\
**Post date:** [July 15, 2022, 8:16pm UTC](https://forum.inductiveautomation.com/t/replaced-pc-running-edge-and-now-i-cannot-view-my-edge-tags-from-my-central-gateway/61973/2 "2022-07-15T20:16:29Z")

</div>

Check security zones. Depending on how zones are defined, it’s possible your replacement Edge gateway is not falling into the expected security zone.

---

<div class="post-metadata">

**Author:** ![jrod](https://avatars.discourse-cdn.com/v4/letter/j/e480ec/32.png) [@jrod](https://forum.inductiveautomation.com/u/jrod)\
**Post date:** [July 15, 2022, 8:24pm UTC](https://forum.inductiveautomation.com/t/replaced-pc-running-edge-and-now-i-cannot-view-my-edge-tags-from-my-central-gateway/61973/3 "2022-07-15T20:24:44Z")

</div>

I have the default security zones on my edge and central gateways.

---

<div class="post-metadata">

**Author:** ![jrod](https://avatars.discourse-cdn.com/v4/letter/j/e480ec/32.png) [@jrod](https://forum.inductiveautomation.com/u/jrod)\
**Post date:** [July 16, 2022, 11:36pm UTC](https://forum.inductiveautomation.com/t/replaced-pc-running-edge-and-now-i-cannot-view-my-edge-tags-from-my-central-gateway/61973/4 "2022-07-16T23:36:28Z")

</div>

The problem turned out to be a licensing problem with the MQTT transmission module. I had to reinstall that module.