This example was not the report module, but if I'm understanding you correctly, the problem seems similar. Perhaps it will help you:

> [@Perspective Alarm Status Table & Event Value column scaling/formatting](https://forum.inductiveautomation.com/t/perspective-alarm-status-table-event-value-column-scaling-formatting/73845/2):
>
> I had an idea on this. I'm not sure how practical it is for your usage case, but I was able to achieve the desired effect by moving the alarm to a derived tag or an expression tag. Example: Actual event value = 82.687545776 Tags: [image] TestTag01 has the raw value and TestTag02 has the expression value Expression: round({[.]TestTag01.value}, 2) Result: [image] Both alarms have the same trigger value, but TestTag02 displays with only two decimal places. Here is how that looks in a der…

---