Hi guys,

A quick simple one; is there any way to retrigger an alarm through the alarm pipeline if it’s sat active for a certain amount of time and not been cleared? We monitor a bunch of remote sites and rely on dial-out email alarm notifications to alert us when there is a fault, sometimes guys are missing the single alarm instance and it gets overlooked for large periods. Hoping there’s a simple way to say if an alarm is active for an hour and unacknowledged, retrigger email alarm notification.

I can alternatively do the same thing in the PLC, but it means amending the logic in about 30 different PLCs.

Thanks

---

<div class="post-metadata">

**Author:** ![josborn](https://avatars.discourse-cdn.com/v4/letter/j/4bbf92/32.png) [@josborn](https://forum.inductiveautomation.com/u/josborn)\
**Post date:** [April 30, 2022, 12:17am UTC](https://forum.inductiveautomation.com/t/retrigger-alarm-notification/59080/2 "2022-04-30T00:17:46Z")

</div>

I think what you want is done similar to an escalation pipeline, with a second notification block with a delay before it.

---

<div class="post-metadata">

**Author:** ![mcgheeiv](https://avatars.discourse-cdn.com/v4/letter/m/71c47a/32.png) [@mcgheeiv](https://forum.inductiveautomation.com/u/mcgheeiv)\
**Post date:** [April 30, 2022, 12:34am UTC](https://forum.inductiveautomation.com/t/retrigger-alarm-notification/59080/3 "2022-04-30T00:34:51Z")

</div>

You can also set a delay then loop back to the original notification block.

---

<div class="post-metadata">

**Author:** ![benw](https://avatars.discourse-cdn.com/v4/letter/b/8edcca/32.png) [@benw](https://forum.inductiveautomation.com/u/benw)\
**Post date:** [April 30, 2022, 12:51am UTC](https://forum.inductiveautomation.com/t/retrigger-alarm-notification/59080/4 "2022-04-30T00:51:13Z")

</div>

Perfect, I’ll look into both of those options.  
Thankyou!